A hospital test 25% of their fire alarm system every quarter because of the size of the building...is this acceptable?

I'm sure BS 5839 states it should all be tested every 6 months otherwise it doesn't comply...then again I've been sure before!!

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Testing fire alarms
« Reply #1 on: May 20, 2009, 04:29:20 PM »
A hospital test 25% of their fire alarm system every quarter because of the size of the building...is this acceptable?

I'm sure BS 5839 states it should all be tested every 6 months otherwise it doesn't comply...then again I've been sure before!!
Thats what the code says but then it is only a recommendation.
We're not Brazil we're Northern Ireland.

Offline Dragonmaster

  • Full Member
  • ***
  • Posts: 118
Re: Testing fire alarms
« Reply #2 on: May 20, 2009, 04:57:10 PM »
I'm happy to accept a 12month turn around where there are large numbers of detectors. It's nice to see tests actually being done.
"Never do today what will become someone's else's responsibility tomorrow"

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Testing fire alarms
« Reply #3 on: May 20, 2009, 07:06:05 PM »
5839 states that the interval between service visits should not exceed 6 months (two visits minimum),meaning that you can do 50% each visit over a 12 month period giving you 100% annually (most of my contracts are still 25%/quarterly visits).However,vented battery systems should be quarterly.
The interval can be increased if it is felt necessary following an assesment (or by customer request) on a case by case basis.
Interestingly,I have just received a copy of the new IS 3218:2009 where the service schedule has been kept at quarterly (as per 1988 5839).

Excerpt from 45.3 of 2002/A2:2008 -

"The period between successive inspection and servicing visits should be based upon a risk assessment, taking into account the type of system installed, the environment in which it operates and other factors that may affect the long term operation of the system. The recommended period between successive inspection and servicing visits should not exceed six months. If this recommendation is not implemented, it should be
considered that the system is no longer compliant with this part of BS 5839".

and from 45.4 -

"NOTE 1 The work described may be carried out over the course of two or more service visits during each twelve month period."

The above relates to the testing of all devices etc. annually