Well Colin, thank you for taking the time to explain things so clearly and concisely to all of us mere ignorant fire alarm engineers.
I would reply to some of your comments as follows:
1) It is precisely those people who have read a copy of 7273-4 that are complaining that it is difficult to understand. Not those who have only heard rumours about it. I also think it is unfair to infer that I am not 'professional' because I don't understand it and can't unravel all it's mysteries even after reading it many times. I normally have very few problems understanding these sort of documents. Furthermore, I can't recollect one person posting on this forum, apart from yourself, that claims that 7273-4 is straightforward and simple to understand!
2) You continually go on about the need for the Standard. I can't remember anyone (and certainly not myself) arguing against this need. Your emotive descriptions of people being trapped in a burning building are therefore superfluous.
3) If, as you say, the monitoring of software faults and indeed all the other long list of fault monitoring requirements, is automatically met by any panel meeting BS 5839-1 (is this the right BS?)/EN 54-2 then why bother listing all of these requiremnts in BS7272-4? Why not just, or alternatively also, state in BS7273-4 that this is so. I am afraid that, despite your beliefs that they should, very few fire alarm engineers learn all the BS recommendations for the requirements intrinisic in manufacturing a control panel. This is normally the job of the panel designer. Those of us that 'fret' about the specifics of BSs are those who are trying to make them work.
4) I have recently contacted 5 well-known control panel manufacturers regarding this standard. Two have already replied. Both said that BS7273-4 is an 'installation standard' and therefore they have not read it and are not that interested in it.
I asked them both, if any equipment in their range met all the recommendations of BS Clause 5.1.1. Both said that they 'thought they probably did' apart from the recommendation for monitoring disablements. Therefore neither, despite your assertions, that any fully BS compliant panel available today would meet the BS7273-4 interfacing recommendations, these two appear not to.. At the very least, a disablement on their control panels did not provide a signal that could be used to interface into a BS7273-4 system.
The other three well known panel manufacturers have not yet replied. I wonder why not? I would have thought that if they had a panel that was fully suitable for use with BS7273-4 they would be shouting it from the rooftops.
5) I still do not understand your explanation of my previous comments regarding the critical signal path comment. I appreciate that it is probaly just me who is too stupid to understand it and I will refer to BS7273-4 to try to rectify my ignorance. Alternatively, I await explanation from other members of Firenet.
6) I have previously asked you to identify the addressable loop powered interface that could be used in BS7273-4 systems that I understood you claimed was currently available. Are you yet able to do so for the benefit of all us ignorant fire alarm engineers who are desperately trying to work out what it could be? Again, I'm surprised that it's manufacturers are keeping it so secret.
If you find any of the above to be be written in a sarcastic tone, I can only offer the playground defence of 'well you started it'