Author Topic: Open cloakroom on a dead end corridor in a school  (Read 6301 times)

Offline SidM

  • Jr. Member
  • **
  • Posts: 92
Open cloakroom on a dead end corridor in a school
« on: July 03, 2009, 11:10:21 AM »
A door is impractical because you would lose the space and the little blighters could hide in the cloakroom and play funny games.  In such a situation what is the fastest acting detector head that could be used in the cloakroom.  Is it acceptable to use ionising or do you have to use optical?
"We are the unwilling,
Led by the unqualified,
Doing the unnecessary,
For the ungrateful.
-Living the dream!"

Offline Big A

  • Full Member
  • ***
  • Posts: 199
Re: Open cloakroom on a dead end corridor in a school
« Reply #1 on: July 03, 2009, 11:25:13 AM »
I'd go for a drencher system. That'll teach the little blighters.

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Open cloakroom on a dead end corridor in a school
« Reply #2 on: July 03, 2009, 12:09:59 PM »
Cloakrooms are high risk rooms in schools and must be separated from escape routes by fire resisting construction.  No ifs, no buts...

Stu


Offline Dinnertime Dave

  • Hero Member
  • *****
  • Posts: 819
Re: Open cloakroom on a dead end corridor in a school
« Reply #3 on: July 03, 2009, 12:50:12 PM »
Cloakrooms are high risk rooms in schools and must be separated from escape routes by fire resisting construction.  No ifs, no buts...

Stu



Cloakrooms are potentially high risk but I would be happy to accept any of the following -

1.   Separation by fire resistance
2.   Smoke detection
3.   Provide an alternative from classrooms thus removing the dead end/inner room 



Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Open cloakroom on a dead end corridor in a school
« Reply #4 on: July 03, 2009, 04:19:48 PM »
CLG Guide:

"Cloakrooms should not form part of circulation spaces and where this is not possible you should consider using lockers made from a non-combustible material."

Detection is insufficient compensation.

Stu


Offline Clevelandfire 3

  • Hero Member
  • *****
  • Posts: 566
Re: Open cloakroom on a dead end corridor in a school
« Reply #5 on: July 04, 2009, 12:23:31 AM »
Detection is not a viable solution

Either alternative means of escape should be provided from each classroom or cloakrooms should be seperated from escape route.

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Open cloakroom on a dead end corridor in a school
« Reply #6 on: July 04, 2009, 11:28:00 AM »
Thanks Clevelandfire 3 (what happened to 1 and 2?).

Just a further point - even if an alternative escape route is available for all, it is usually still a bad idea to have the cloakroom in a circulation space because of its vulnerability to arsonists.  With schools we are interested in much more than just life safety and high fire loads should be kept out of circulation spaces.  Of course, this is dependent upon the general arson threat to the school, but it is high for many schools and is never zero.

Stu