Hi Wiz
I quote:
BS5839-1, clause 20.2. e. The figures of 45metres and 30 metres quoted in d) should be reduced to 25m and 16m respectively in th following circumstances:
1) where a significant proportion of occupants have limited mobility and it can reasonably be anticipated that one of these occupatns will be the appropriate person to first operater the fire alarm system in the event of fire; or
2) where processes in the area result in the liklihood of rapid fire development (e.g. where there is use, of processing, of highly flammable liquids of flammable gases).
I think that clarifies
Now I'm off for some shut eye - check in tomorrow.
mevans421, you are correct about part 2) of your explanation. I never had my BS with me and I was quoting from memory and I forgot about the second sub-clause. it is included along with the 'limited mobility' reasons as a need to reduce travel distances.
However, I still think your original explanation could be misunderstood. I read your original post to mean that distances are
always reduced to 16m for the reasons of the second sub-clause.
I quote the part of your post that says this:
The above distances should be shortened to 25metres where a significant number of people are likley to be mobility impaired and shortened again to 16 metres if processess in the area are likley to result in rapid fire spread in the event of ignition.This is not how I read the BS.
My undersatnding is it needs to be reduced (for both reasons) to only 25m if the actual travel distance can be calculated and to 16m 'straight line distance' if it can't be pre-calculated (at design stage).
I'm off to earn some money - check in later