Thank you Wiz.
I still fail to see why the system would not work.
If the FA system interlock worked, then job done.
If the FA system did not work then push the button that they do every day to open the door.
If the power fails, job done.
FSO, the 'normal' exit switch you are talking about is the switch I call the 'Request To Exit' Switch.
Firstly, not all doors have a Request To Exit switch i.e some electronically locked doors are only to be used in an emergency and have no switches.
Secondly, not all 'Request To Exit' switches are wired in 'series' with the power feed to the locking device. The ones that are, are those which unlock the door only as you depress the switch and where the door locks again immediately when you release the switch. If you had this type of switch you could possibly argue that it is only doing the same thing as the 'green box' (which I call the Emergency Door Release) would do i.e breaking the power feed to the locking device. However all Emergency Door Releases meeting BS7273-4 recommendations need to be double pole and your RTE switch would also have to be double pole for the following safety reasons; Whilst it is true that an accidental disconnection of the wiring to a single pole RTE switch would release a fail-safe release mechanism, an accidental short of the wiring to a single pole RTE would actually short out the switch contacts and keep the release mechanism energised even when the RTE was operated!! The double-pole requirement is meant to avoid short circuits allowing this to happen.
Thirdly, many RTE switches are not wired as above. With the above scenario, it can be annoying when the door locks immediately you release the button (i.e if you are carrying something you have try to press the RTE switch with your elbow and open the door with your foot before you release the switch!)
The method of connecting RTE switches asscociated with a keypad/or proximity reader on the entrance side of the door is different. They normally have dedicated connection terminals for a RTE switch. If you wire the RTE to these terminals what happens, is that when you operate the RTE switch, it opens the door for the same period of time programmed into the keypad/reader controller for 'door open' time. i.e. pressing the RTE button causes the system to unlock the door for the same pre-programmed period of time as if someone has entered the correct code into the keypad/shown a valid token to reader that is on the entry side of the door. This makes the door much easier to use, press the RTE and the door stays unlocked for a few seconds.
However, the type of RTE switch usually required for this connection method is a Normally Open switch. This means its wiring is not monitored for disconnection i.e. a wire disconnecting from it won't cause the lock to fail-safe door open. Furthermore it is relying on the controller to accept the signal from the RTE switch and open the door. If the controller failed the door wouldn't open. In both these circumstances it is imperitive that a double pole Emergency Door Release is also provided and wired into the power feed to the door locking device. You certainly couldn't rely on just the RTE switch.