Author Topic: Heat resistant wiring to BS standard?  (Read 18385 times)

Offline GregC

  • Full Member
  • ***
  • Posts: 180
Re: Heat resistant wiring to BS standard?
« Reply #15 on: December 17, 2009, 12:40:07 PM »
But do they need to be red?

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2493
    • http://www.firewizard.co.uk
Re: Heat resistant wiring to BS standard?
« Reply #16 on: December 18, 2009, 12:01:10 AM »
The reality is not all protected cabling is in red (if orange of older types), which makes identifying how a system has been wired more difficult - found a system completely in white which started bells ringing in my head, but after painstakingly examining the wiring to find a decipherable bit of parking (embossed, not printed so difficult to read) it was Pirelli FP200 Gold.

Other times red wires are used, but get painted for aesthetics
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: Heat resistant wiring to BS standard?
« Reply #17 on: January 28, 2010, 12:12:25 PM »
Well, one thing is for sure; the installation doesn’t comply with current good industry practice.  Is this OK?  The fact is that it is the School’s decision as to whether it is or not.  They can’t expect safety kit to last forever, so renewal should at least be considered (and if the risk is assessed and it’s reasonably practicable to do it, then it must be done – “we can’t afford it” is no protection from that legal requirement).

At the very least, they know about it now, so they must review their fire risk assessment to determine whether it’s acceptable.  They could use the guidance in the Fire Safety Order Guide on ‘Fire Safety Risk Assessment - Educational Premises’ – if they conclude that the system provides all the F, D&A functionality recommended in Parts 1 and 2 of the Guide, then it might be that then can make a case that it is acceptably safe?

All the above assumes that the system is in ‘steady-state’ maintenance – if they modify it then that would make the case for retaining the non-compliant system weaker.

Finally – this is a school; the biggest risk tend to be arson and the most likely outcome is significant property loss or damage.  There might be a case for renewal due to the enhanced asset protection that a compliant system might offer?

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: Heat resistant wiring to BS standard?
« Reply #18 on: January 28, 2010, 12:21:29 PM »
Well, one thing is for sure; the installation doesn’t comply with current good industry practice.  Is this OK?  The fact is that it is the School’s decision as to whether it is or not.  They can’t expect safety kit to last forever, so renewal should at least be considered (and if the risk is assessed and it’s reasonably practicable to do it, then it must be done – “we can’t afford it” is no protection from that legal requirement).

At the very least, they know about it now, so they must review their fire risk assessment to determine whether it’s acceptable.  They could use the guidance in the Fire Safety Order Guide on ‘Fire Safety Risk Assessment - Educational Premises’ – if they conclude that the system provides all the F, D&A functionality recommended in Parts 1 and 2 of the Guide, then it might be that then can make a case that it is acceptably safe?

All the above assumes that the system is in ‘steady-state’ maintenance – if they modify it then that would make the case for retaining the non-compliant system weaker.

Finally – this is a school; the biggest risk tend to be arson and the most likely outcome is significant property loss or damage.  There might be a case for renewal due to the enhanced asset protection that a compliant system might offer?

Schools in your area sound rough!!

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: Heat resistant wiring to BS standard?
« Reply #19 on: January 28, 2010, 12:44:55 PM »
Couldn't say - I've stopped hanging around them since the Injunction.

On a serious note the Arson Prevention Bureau quote statistics that around half of school-time fires are arson attacks and 63% of all fires in schools are started maliciously (http://www.arsonpreventionbureau.org.uk/Publications/Files/EducationUnderThreat.pdf).