TW, I believe they mean 'fire resistant' rather than 'heat resistant'.
The recommendation for fire resisting cable on the 'detection' element of fire detection and alarm systems appeared in the 2002 standard.
The recommendation for a fire resisting wiring system on the 'alarm' element of fire detection and alarm systems goes back much further, I believe to about 1970.
However, British Standards are not retrospective, so if the wiring system met the Standard at the time of installation, then there is no automatic need to meet a new recommendation when it is introduced.
The term 'wiring system' above is used because earlier standards accepted the use of non-fire resistant single insulated cables within metal conduit etc. to be acceptably fire resistant in many circumstances (not the case with current Standards).
I would also say that if the fire alarm system is over, say, 30 years old then it must be getting to the stage where replacement, with a view to embracing modern equipment and fault monitoring techniques etc., should be a considered a real benefit even if the old system hasn't actually failed and met the BS recommendations at the date of installation.