Author Topic: Combined fire alarm and intruder alarm.  (Read 20880 times)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: Combined fire alarm and intruder alarm.
« Reply #15 on: March 04, 2010, 04:48:07 PM »
Thanks Guys

It is a part 1 system and the RP has decided to be looking to update their system soon. (His Words) Thanks again.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Chris Houston

  • Guest
Re: Combined fire alarm and intruder alarm.
« Reply #16 on: June 15, 2010, 11:44:57 PM »
Is it acceptable to have a combined fire alarm and intruder alarm or must it be two totally separate systems. ??? It is also connected to a ARC

In the UK, there is not law that prohibits it, but hard to imagine how 1 system would comply with BS 5839 (fire) and BS EN 50131 (intruder).  Does it?