Author Topic: Variations from BS  (Read 30381 times)

Midland Retty

  • Guest
Re: Variations from BS
« Reply #15 on: April 08, 2010, 04:07:00 PM »
Thanks men... it's all interesting stuff and tis true I'm completely frustrated !!

TW you're right in what you say and and it would all work "by the book" if we were working directly for the end user and we could converse in writing and tell them to talk to their insurer and explain the reasoning behind design issues etc etc etc .

But I suppose what I'm griping about really is the fact that when you're involved in any "large" job that involves Electrical contractors/M&E contractors god knows how many design teams /Arcitects /Consultants etc, then we become the tadpole at the end of the food chain swimming amongst sharks.

And it doesn't matter how much we spout the BS and tell everyone what their roles should be and what BS says we should all do, basically no one else gives a monkeys except us !

.... and apart from all that, it just seems quite difficult to apply this bit of the BS to a real world scenario....:)


Hi David

I can understand why you are frustrated, and its a common problem.

As TW said all you can do is cover your back, inform them that what they are getting isn't compliant (In writing) and if they choose to ignore you then on their heads be it!

Graeme

  • Guest
Re: Variations from BS
« Reply #16 on: April 08, 2010, 06:01:06 PM »
And it doesn't matter how much we spout the BS and tell everyone what their roles should be and what BS says we should all do, basically no one else gives a monkeys except us !



bingo. thats it in a nutshell Dave.

Large installs as mentioned are the worst

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Variations from BS
« Reply #17 on: April 08, 2010, 10:01:37 PM »
Thanks men... it's all interesting stuff and tis true I'm completely frustrated !!

But I suppose what I'm griping about really is the fact that when you're involved in any "large" job that involves Electrical contractors/M&E contractors god knows how many design teams /Arcitects /Consultants etc, then we become the tadpole at the end of the food chain swimming amongst sharks.

And it doesn't matter how much we spout the BS and tell everyone what their roles should be and what BS says we should all do, basically no one else gives a monkeys except us !

.... and apart from all that, it just seems quite difficult to apply this bit of the BS to a real world scenario....:)


Your frustrations as an alarm engineer mirror mine as a fire risk assessor. Invariably we come across half baked ill considered mix and match solutions to fire safety in which all contributors are responsible only for their element and nobody looks after the bigger picture and co-ordinates things to ensure that everybody is rowing in the same direction.

Sometimes the mistakes are so obvious and fundamental you cannot imagine why the qualified engineers do not pick it up and get it dealt with, usually the response is its someone elses problem and not in my contract. Nobody is thanked for rocking the boat.

No wonder I have no hair left and look 56 when I am really only 28.

I remember one top flight brand new  football stadium with every possible bell and whistle - trouble was every body had taken their supply for their equipment from the same circuit and nobody had done the simple sums. I raised it from a fire point of view asking simple firemans questions  and was roundly criticised - you are a fireman stick to fire, keep your nose out and leave the electrical side of things to us engineers. On the first match the circuit breaker melted, the floodlights cameras and PA all died. 

Another industrial plant handling ethanol - the plant was beautiful but required zoning under the DSEAR Regs, nobody told the fire alarm designer of this simple fact, or the ventilation engineer who sourced his make up air for another area from the hazardous zones, and nobody took the sprinkler system flow into account when designing bunds.

Now- soap box out- What are the contributory factors?
Poor standards of design and project management, too much fragmentation and sub contracting for sure. But then

Do we still have Clerks of works?
Is the Building Control system part of the problem?
Or is it the Design and Build concept?
Do QA schemes for contractors really make any difference?
Are Approved inspectors in the pockets of the developers?
Do the different definitions and role of duty holders under the CDM Regs compared to those under the Fire Safety Order contribute?
Should the Designers, Principal Contractors and CDM Co-ordinators be defined as persons having control and held responsible under the Fire Safety Order at least for the warranty period of the building? Now that would make a difference!
 

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Variations from BS
« Reply #18 on: April 09, 2010, 09:00:05 AM »
Prof., I've met some Bozos in my time in this game but never an electrical design engineer who didn't know anything about electrical distribution systems!!

It is the lifeblood of any electrical engineer and the basis of all initial calculations; First, is the electrical supply to the premises of sufficient capacity? Secondly, calculate cable sizing and fusing requirements for the electrical supply distribution.

Are you sure they hadn't used the club's centre-back clogger as their design engineer?

I agree with you that all too often all the different elements of a project stick rigidly to their own areas, knowing that raising questions and concerns about something that is not seen as being their responsibility will only 'rock the boat' and work against them in the long run. It is almost always better (financially to yourself) to ignore obvious problems in other people's responsibilities and let them take the flack when the proverbial hits the fan (or fuses the lights!)

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Variations from BS
« Reply #19 on: April 09, 2010, 09:53:17 AM »
Thanks men... it's all interesting stuff and tis true I'm completely frustrated !!

But I suppose what I'm griping about really is the fact that when you're involved in any "large" job that involves Electrical contractors/M&E contractors god knows how many design teams /Arcitects /Consultants etc, then we become the tadpole at the end of the food chain swimming amongst sharks.

And it doesn't matter how much we spout the BS and tell everyone what their roles should be and what BS says we should all do, basically no one else gives a monkeys except us !

.... and apart from all that, it just seems quite difficult to apply this bit of the BS to a real world scenario....:)

Is the Building Control system part of the problem? 
Yes. I certainly think that there is a general lack of knowledge in BC when it comes to fire seperation.
Had another issue last week with a brand new build. BC had been day before for final inspection and picked up a 50mm high threshold "step" at a final exit from stairway enclosure. Wasn't right from point of view of wheelchair users but accepted it as there was two other exit routes out of the enclosure.
I had a look above false ceiling in same stairway and found smoke stopping around plastic pipework & trunking ok but no fire stopping. And this is an enclosure containing a wheelchair refuge.

Commencement of FSO in NI posponed for number of reasons and I understand one being BC not happy that they may lose some work. (Can't think why they didn't flag it up at consultation stage.) But from my dealings with new builds & BC there is certainly  a training need.
That coupled with the ongoing depletion of experience in FS Depts there are interesting times ahead.
Is it just me being too fussy or is a lot of a FRA more like a snagging list?
We're not Brazil we're Northern Ireland.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Variations from BS
« Reply #20 on: April 09, 2010, 10:51:00 AM »


Prof., I've met some Bozos in my time in this game but never an electrical design engineer who didn't know anything about electrical distribution systems!!

It is the lifeblood of any electrical engineer and the basis of all initial calculations; First, is the electrical supply to the premises of sufficient capacity? Secondly, calculate cable sizing and fusing requirements for the electrical supply distribution.

Are you sure they hadn't used the club's centre-back clogger as their design engineer?


Dr Wiz the problem in that case was too many sub contractors each only looking after their own bit and a lack of overall management and supervision of what was happening at the right level.

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Variations from BS
« Reply #21 on: April 09, 2010, 11:24:55 AM »

Dr Wiz the problem in that case was too many sub contractors each only looking after their own bit and a lack of overall management and supervision of what was happening at the right level.

And I don't think anything has ever changed on any job ever since, it's every man for himself.

Fire detection and alarms are still generally seen as just a necessary evil and generally at the bottom of everyone elses list.

I think this "talk to all interested parties" stuff is too vague on these larger jobs and if there is going to be provision to do things differently from the "Standard" there needs to be a clear statement of who is taking responsibility for the fire detection system from the client's perspective at building stage perhaps written into the Building Regs.

I know this is probably written into the BS about defining roles but it's no good when no one else in the world has read it or cares.
« Last Edit: April 09, 2010, 11:26:43 AM by David Rooney »
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Midland Retty

  • Guest
Re: Variations from BS
« Reply #22 on: April 09, 2010, 11:50:37 AM »

Dr Wiz the problem in that case was too many sub contractors each only looking after their own bit and a lack of overall management and supervision of what was happening at the right level.

And I don't think anything has ever changed on any job ever since, it's every man for himself.

Fire detection and alarms are still generally seen as just a necessary evil and generally at the bottom of everyone elses list.

I think this "talk to all interested parties" stuff is too vague on these larger jobs and if there is going to be provision to do things differently from the "Standard" there needs to be a clear statement of who is taking responsibility for the fire detection system from the client's perspective at building stage perhaps written into the Building Regs.

I know this is probably written into the BS about defining roles but it's no good when no one else in the world has read it or cares.

I used to be a mechanical services engineer, and the problems you described are typical of any major project. I wouldnt say its every man for themselves however.

Instead there is often so much going on that even the most seasoned project managers are unable to co-ordinate it all effectively. Trying to get Joe Bloggs on site to meet with John Smith is difficult as subbies are often all over the place on other jobs in between popping back to site to do their bit.

Time costs money and subbies cant afford to turn down other work simply to attend a site meeting.

This leads to cock ups, things get missed or left out, and all the usual trappings that go along with it can snowball.

This is why detailed plans and comprehensive job specs are crucial.




Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Variations from BS
« Reply #23 on: April 10, 2010, 10:21:36 PM »


In any event I can't understand your comment of a L1/P1 category only applying to property protection.


You're generalising my specific comments.  This building is a museum.  It is likely to have lowish fire loading, highish ceilings and valuableish contents.  I was guessing that the lack of detection in a lantern light, high in a ceiling, might not entirely jeapordise means of escape but might lead to increased damage due to delayed detection out of hours when no one is around.


Stu, the requirement for detection in lantern lights (within a protected area) has nothing to do with the category of a system.

 

Who said this is in a protected area?


Stu


Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Variations from BS
« Reply #24 on: April 12, 2010, 10:53:29 AM »


In any event I can't understand your comment of a L1/P1 category only applying to property protection.


You're generalising my specific comments.  This building is a museum.  It is likely to have lowish fire loading, highish ceilings and valuableish contents.  I was guessing that the lack of detection in a lantern light, high in a ceiling, might not entirely jeapordise means of escape but might lead to increased damage due to delayed detection out of hours when no one is around.


Stu, the requirement for detection in lantern lights (within a protected area) has nothing to do with the category of a system.

 

Who said this is in a protected area?



Stu

Your earlier post said 'I believe the detection in the lantern light is required solely for the L1/P1 classification.   So its purpose is not to protect life but to protect property' 

The L1 part of the catetgorisation relates to Life. I can't see why you said So its purpose is not to protect life but to protect property .[/b] Surely, the detection recommended is equally important for the protection of Life as it is for the protection of property where the category includes the L designation?

The term 'protected area' in this BS clause and context means the lantern light is in an area that requires automatic detection. Whilst the clause is mentioning lantern lights in general it doesn't mean that every lantern light in every situation in every building requires protection. Only those in 'protected areas'. It therefore also means that in the circumstances that no automatic detection is required in an area (unprotected area), then even if that area  has a lantern light then it doesn't require anything in the lantern light even though the clause seems to mention lantern lights in general. The lantern light in this query is in a 'protected area' (the area has beam detectors fitted and an L1/P1 system has detectors virtually everywhere anyway) so the clause applies.

Your earlier post said I believe the detection in the lantern light is required solely for the L1/P1 classification. The point I was making in my reply was that the requirement equally applies if it is, say L3 or P2 and not solely L1/P1 category. If the lantern light is in a 'protected area' the lantern light may also need automatic detection.

I am not being pedantic, Stu. If there is any chance of confusion in the way posts are written, I think it is important to clarify things for all readers.

« Last Edit: April 12, 2010, 11:01:12 AM by Wiz »

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Variations from BS
« Reply #25 on: April 12, 2010, 06:34:54 PM »
Fair enough. 

To me the name of the category of the system is of secondary importance after its purpose.  The fact that this one is supposedly designated L1/P1 tells me a little about its purpose but it is possible to glean more about the purpose of different parts of the system from the nature of the building.  The facts about the building tend to indicate to me that some of the detection is for property protection and not solely for life protection.  I don't know but I would still suspect that the advantages to be gained from the lantern light detection would be in terms of property protection and not life.  Maybe David will elucidate us on this point.  I'm not a great one for putting detection where it will serve no useful purpose.

Stu


Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Variations from BS
« Reply #26 on: April 13, 2010, 09:44:10 AM »
I think the BS recommendation for possible automatic detection in a lantern light is all to do with the volume of smoke that could be contained within that lantern light (without detection in it) before it 'spilled out' and reached the automatic detection on the ceiling level. The BS recommendation's mention of only lantern light's of a certain size seems to support this.

One would assume that the amount of smoke taken to fill a large lantern light (without detection in it) is probably proportional to the size of the fire. Therefore if the lantern light is very big it will take a lot of smoke to fill it before the smoke spills out and reaches the automatic detectrion on the normal ceiling level. At this point the fire may be very big.

So BS recommends automatic detection in lantern lights over a certain size to provide detection earlier than would otherwise happen with only ceiling level detection.

Also, the actual installed detection mentioned in this post is beam detectors. These could be mounted up to 600mm below the ceiling level. I would suggest that much more smoke would be needed to fill the lantern light, overspill into the 'room' and then fill up the 600mm gap than would be needed to reach point style automatic detectors which might have sensing chambers only 50mm below the ceiling level.

I think any earlier warning of smoke could be considered equally as important in both Life and Property category systems and I think it applies to the system that is mentioned in this thread because it has been designated a category of L1/P1. In fact, I would suggest that the L part of the category is the most important if a life is considered more important that a museum exhibit. Even BS allows higher ceiling limits (lower response times) to automatic detection in just P systems. Surely everythings points to L being more important than P!

At this point, I would confirm that the BS recommendation also calls for automatic detection in any size lantern light where it is also used for ventilation (even opening windows?) because, I assume, it believes the air-flow in a fire is likely to take any smoke away from the ceiling-mounted detection and therefore a detector is always required very close to the point of potential ventilation..

I don't disagree with Stu's principle that every situation needs to be looked at individually to ascertain how important any BS recommendation might be to that application. If the benefits are far outweighed by the cost then there might be grounds for ignoring the recommendation. However, BS also recommends that a proper 'agreed variation' is sought for this BS non-compliance. BS explains exactly what is considered to be an 'agreed variation'.

I don't agree that just because this building is a museum that the fire detection system is automatically primarily designed for the protection of property. But even if it was, the automatic detection requirements would be virtually the same (other than the maximum ceiling height limits mentioned above). There are no big differences in the BS requirements for location of automatic detection in a L1 or P1 system. P systems generally only differ from L systems in that they may have longer standby battery duty and automatic off-site signalling.


Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Variations from BS
« Reply #27 on: April 13, 2010, 12:32:04 PM »
I think we are all getting too hung up on whether the lantern light needs protection or not.... that wasn't the issue.

But for what it's worth, the objective of a Category L1 or P1 system is to offer the earliest possible warning of fire, therefore to me that means a detector is required in the lantern light for all the reasons quoted by Wiz above and simply because the objective of the category calls for it along with all teh other reasons I quoted earlier.

My question/gripe is that we could have anyone of several people including the QS, consultant, client, arcitect etc stop us from installing this device and by doing so we no longer meet the objective of the category.

This to me is a bit deeper than mounting a call point at 1000mm from ffl.
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic