John it was included in the 1965 Building Regulations so you can discount any major fires after that date. It may have been in one or more of the local bye laws that created the National Building Regulations for E&W the Scots beat us to it again.

Extract from 1965 BR.
E13.- Fire-stopping
(1) Any fire stop required by the provisions of this so formed and positioned as to prevent or retard the passage of flame.
(2) Any fire stop shall
(a) if provided around a pipe or duct or in a cavity, be made of non combustible material or (if it is in a floor or wall constructed of combustible material) of timber not less than l ½ inches thick, and
(b) if provided around a pipe or duct, be so constructed as not to restrict essential thermal movement.
(3) Any fire stop formed as a seal at the junction of two or more elements of structure shall be made of non-combustible material if all such elements are required by this Part to be non-combustible.
(4) Any cavity in an element of structure which¬
(a) is continuous throughout the whole or part of such element, and
(b) has a surface of combustible material exposed within the cavity which is of a class lower than class O in regulation E14,
shall be fire stopped
(i) at any junction with another element of structure or with a ceiling under a roof: and
(ii) in such a position that there is no continuous cavity (without a fire stop) which in one plane exceeds either 25 feet in a single dimension or 250 square feet in area,
but nothing in this paragraph shall prohibit the insertion of combustible filling in a cavity.