Author Topic: On line Fire Risk Assessments  (Read 34438 times)

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: On line Fire Risk Assessments
« Reply #15 on: August 02, 2010, 08:40:24 AM »
Bit like a surgeon guiding the house porter through a surgical procedure on line.
The surgery still isn't being performed by a competant person.
We're not Brazil we're Northern Ireland.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2493
    • http://www.firewizard.co.uk
Re: On line Fire Risk Assessments
« Reply #16 on: August 02, 2010, 01:02:25 PM »
A large part of the problem is due the CLG guidance notes, it is a common perception that anyone can carry out a fire risk assessment all they have to do is follow the guides or get hold of a bootleg checklist from PAS 79.
 

If people actually bothered to use the full DCLG guides at all (not just the introductory booklet) and the further references therein things would be better, few people even apply these, especially with the Yes/No/NA type assessments.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Mr. P

  • Hero Member
  • *****
  • Posts: 685
Re: On line Fire Risk Assessments
« Reply #17 on: August 02, 2010, 02:10:58 PM »
Mike, the format of RA, if it covers all requirements of rro, then does it matter where it comes from? But yes! The person carrying out the RA must be competant et al.

Are we not over complicating this issue?

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: On line Fire Risk Assessments
« Reply #18 on: August 02, 2010, 07:46:09 PM »
Mr P I agree, if as you say it is a good format, it doesn't matter where it comes from. The point I am making is that it is the competency of the person doing it that is crucial.
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: On line Fire Risk Assessments
« Reply #19 on: August 02, 2010, 08:50:12 PM »
Are we still discussing online FRA's because my understanding of an online FRA is the website asks the RP a questions the RP answers and the website produces the FRA. No matter how good the website is or its format what questions can they ask to ensure they get the right answers without being on site. Unless the RP is competent in fire safety then he wouldn't need them and could download a free FRA template to save a couple of quid.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: On line Fire Risk Assessments
« Reply #20 on: August 03, 2010, 09:15:20 AM »
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline BLEVE

  • Sr. Member
  • ****
  • Posts: 324
Re: On line Fire Risk Assessments
« Reply #21 on: August 03, 2010, 09:53:40 AM »
I agree with much of the article. However, disagree with the detail wrt cause & effect programming, false alarm criteria (OTT)etc
it would be s&s to ensure compliance with BS 5839 plus demonstrable maintenance.



Offline Tom W

  • Hero Member
  • *****
  • Posts: 603
Re: On line Fire Risk Assessments
« Reply #22 on: August 12, 2010, 03:05:09 PM »
My problem with them in is you have so much faith in the fact the assessor understands the question properly.

AND

If you are completing an online risk assessment you would probably be sat at a desk. Thats not the best place to be when assessing a building especially for a novice