Poll

Having read the determination based on the advice of Sir Ken Knight, and taking into account the circumstances of that case, was Sir Ken right to advise that the heat detectors satisfied the FSO.

Yes. Sir Ken was very wise.
No, Sir Ken was wrong.
I really don't care
I do not trust the determination process in any case

Author Topic: Sir Ken Knight considers that heat detectors in bedroom of a hotel meet the FSO  (Read 44803 times)

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
I know that this landmark determination was discussed elesewhere, but it has come to my notice that people are finding it difficult to locate the determination on the CLG website.  It has even been rumoured that there are those who would rather you did NOT know about it, though, personally, I think that this is just scurrilous mischief.

So, to help and remind people about it, here is what Sir Ken, a man who is very WISE on such matters actually said in his sound and sage advice to the Secretary of State:

"I have concluded that in this case, the use of heat detectors in the hotel bedroom provides a suitable technical solution to demonstrate compliance with the FSO, and I am advising the Secretary of State accordingly."

Sensible chap or what?

Now do remember that this determination only applies to that one hotel (and thousands of others just exactly the same as it of course). I am currently dealing with an old listed building where shortfalls in MoE and structural fire precautions justifies using smoke detectors in bedrooms, but that is what risk assessment is all about.

Anyhow, just in case there is any truth that some people would rather forget about this determination, do be sure to tell all your friends and make sure everyone knows about it, as it is important that they do.
http://www.communities.gov.uk/publications/fire/hotelfiredetection
To help everyone find it, here is the link:





NOTE TO MODERATOR: Is it ok for me to post this on other topics, such as fire risk assessment?

« Last Edit: September 12, 2010, 08:23:44 PM by colin todd »
Colin Todd, C S Todd & Associates

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
NOTE TO MODERATOR: Is it ok for me to post this on other topics, such as fire risk assessment?

Colin thank you, I think your point comes across sufficiently loud and clear.

As for posting the identical message on other threads, personally, I think that this is just scurrilous mischief.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Good oh. Does that mean I can go ahead, Big Al? I would not want to breach protocol or incur the wrath of one as great as you. 

PS How do I set up a poll on whether that jolly good egg, Sir K was right?  I for one will lead the voting with a resounding YESSSSSSSSSSSSSSSSSSS
Colin Todd, C S Todd & Associates

Midland Retty

  • Guest
I too think Sir Ken was right. So it's also a yes from me.

The detector in the bedroom is protect the MOE, not the occupant of the room. Studies have shown that even with smoke detection in the room of origin the occupant will still expire.

There will of course be the odd exception here or there.

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Itseems to me that the odd exceptions are those nice FRS chaps who do not understand how the standard was written and what the FA is for.  ( With somwe exceptions of course).

Offline ando

  • Newbie
  • *
  • Posts: 15
Colin it's almost as if Oooor Ken has sat in on your lectures and gained almost infinite wisdom.

Now as one of those FRS chaps (exception, exceptional or otherwise) but certainly open minded, some things seem pretty clear to me.

In an existing situation where heat detectors are in place in bedrooms intended for the fit and able and where the MOE is relatively well protected, I cannot see any reason why a FRS would want to challenge it.

In a hotel without any detection (yes they still exist) then the recommendation from the FRS might well be for smoke rather than heat, as we do have an interest in all the folk in the hotel (even those in the room of origin)..

Where the duty holder or RP still wishes for heat then unless there are separation or MOE issues which have not been fully considered in an FRA, I really don't see that challenging it would be helpful as the solution could be seen as being reasonable in the circumstances.

Reasonable measures in a given set of circumstances are all that are required after all.

It also seems to be another determination where the DH/RP has done their homework and the FRS has clutched at straws and relied on its assumed high status.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
This dispute seems, to me, to have been a request for a determination on the type of detection suitable for rooms used by persons with limited mobility. Am I correct? Or did it go off on a tangent to include all persons in all rooms?

"This conclusion has been reached on the basis that the rooms will continue to be used for sleeping accommodation be people who do not have mobility of other relevant special needs"

Is the request for determination available anywhere?

« Last Edit: September 14, 2010, 11:39:24 AM by nearlythere »
We're not Brazil we're Northern Ireland.

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
NT,

CLG website.  And it was for rooms other than those used as dormitory accommodation and those where the disabled sleep as they require smoke anyway.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
those where the disabled sleep as they require smoke anyway.

Now I'm confused ??? (easy done)

Sir Ken's conclusion was "This conclusion has been reached on the basis that the rooms will continue to be used for sleeping accommodation be people who do not have mobility of other relevant special needs" (Wee bit of spelling and grammar issues in the last bit)
« Last Edit: September 14, 2010, 11:45:51 AM by nearlythere »
We're not Brazil we're Northern Ireland.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
those where the disabled sleep as they require smoke anyway.

Now I'm confused ??? (easy done)

Sir Ken's conclusion was "This conclusion has been reached on the basis that the rooms will continue to be used for sleeping accommodation be people who do not have mobility of other relevant special needs" (Wee bit of spelling and grammar issues in the last bit)

Ah. A eurika moment cometh. After finding my way round the spelling I can now read it.
We're not Brazil we're Northern Ireland.

Offline Demontim

  • Jr. Member
  • **
  • Posts: 65
The Determination came about as consequence of an appeal against an enforcement notice, it being the practice of the company concerned to appeal against any notice served upon it.

The RA (conducted by assosciates of a group which will not be named in the way actors only refer to the scottish play) for the premise was not current, having been conducted under previous legislation and specified that the occupants of a bedroom involved in fire would be lost.

The FRA's view was that the FSOwas introduced to protect all "relevant persons" and this should therefore include the occupants of the room (mobility was not a specific issue).

Point 30 of the determination

 "It is therefore my view that the choice of heat detector over smoke detectors in this particular case has been carried out in accordance with avaliable guidance related to the particular hotel. In conforming to the British Standard, the responsible person has evaluated the risk in the hotel and concluded that the provision of heat detectors is as low as reasonably practical and that the risk presented in the hotel are those envisaged in these documents.

rightly makes reference to available guidance.

However, during informal discussions with CLG post determination there was a suggestion that the available guidance may need to be revisited in order to address this specific issue. It was also made clear that in hindsight the matter should not have gone to determination but should have been dealt with by the courts.


Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2479
    • http://www.firewizard.co.uk
At least heat detection in bedrooms is better than none - the hotel I was in last week in London (part of an international chain where all the hotels are independently owned) still had it's original 70's FP Act conventional system with smokes to corridors only & nothing in rooms (although I had a 6" bell inside my room which kept me happy).

Doors were all rebated type with no strips or seals and decades of warping that meant they were anything but tight fitting - however escape signage had been upgraded...to excess so that once I left my room I could literally go up, down, left or right!

I'd be more worried about the above hotel than one with good FD30S doors and a system that included heats to rooms (where the risk should be low with smoking banned and appliances PAT tested)
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
However, during informal discussions with CLG post determination there was a suggestion that the available guidance may need to be revisited in order to address this specific issue. It was also made clear that in hindsight the matter should not have gone to determination but should have been dealt with by the courts.

Thats an interesting observation. I have always been surprised at the determination process being used as this should only be used where both sides accept that there is a case of non compliance but there is disagreement over the technical solution to be adopted to remedy it. Clearly in this case there was no such agreement in respect of non compliance.

However the courts could not get involved unless an enforcement notice was served. I wonder why the Authority did not take this approach? They obviously felt convinced they could make it stick?

I await the reviewed guidance with interest, though BS5839 was updated as recently as 2008 so is not scheduled for further review for some time.  

To me the biggest problem here is the lack of any credible empirical evidence or learned research to show, one way or the other, the benefit or otherwise of installing smoke detectors in rooms used for sleeping accommodation. My personal gut feeling is that in the event of a fire in the room there must be an increased chance of surviving that fire if a smoke detector is installed. But I have looked for research data on this without success. For me the issue is this. Whilst we have measures of tenability, and could calculate how quickly a room would become untenable and compare this time with the time to detection for both heat and smoke detectors, there is no evidence  on the likelihood that, in the absense of detectors,  a person would be awakened as a result of the fire - ie by the smell of smoke, temperature rise et al. At least none that I have been able to find. But like many of you I have attended fires where the fire stimuli awoke person sleeping when the detectors failed to operate because it was the "wrong" type of smoke.

The other thing that has always struck me as inconsistent  is that BS5839  part 1 and the research documents that underpin it are clear that there is a balance to be drawn between unwanted alarms and life safety, and that the role of the heat detectors is for the protection of the means of escape. But then BS5839 goes on to recommend smoke detection in rooms designated for use by disabled people. I have always thought this inconsistent but assumed that this is so that the managers can attend the room in the early stages of a fire to render assistance. However this is speculation because the underlying reason for this was not explained in detail. If a smoke detector is a compensation for a disability exactly how is that position arrived at? What is the compensation? Earlier detection of fire? or making management aware earlier to they can assist?   Evidence to me which tends to support the argument for smoke detection in general....but in the absence of empirical evidence its hard to move this argument forward.

But I agree with you Colin, Sir Ken did us all a service in at least drawing a line in the sand. Prior to his determination we had huge inconsistencies amongst Fire Authorities.
« Last Edit: September 15, 2010, 07:52:02 AM by kurnal »

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Demon: If it is appropriate to comment, please do try to get the facts straight rather than spread misinformation. To correct you:
1 It is not the practice of the group involved to appeal all enforcement notices. This is sheer rubbish.
2 The fire risk assessment in place at the time in question was carried out by the RP under the FSO.
3. The RA did not specify that occupants of the room would be lost.
4 In accordance with Home Office guidance under the FP Act (and it was for the Home Office that research on the subject was carried out by the Fire Research Station)-guidance that was current the day before the FSO was introduced- disabled bedrooms were fitted with SD to compensate for their disability.
5. I imagine the informal discussion to which you refer was the all pals together meeting from which invited members of the public who were not F&RS were (strangely) excluded temporarily. Nothing like transparency and openess eh?

Anyway, just remember the good words of Sir Ken, namely that the heat detectors in the case in question satisfied the FSO. Not that they just satisfied guidance. Not that they just satisfied BS 5839-1. THAT THEY SATISFIED THE FSO!!!  I am with Sir Ken all the way. Yep, he definitely got it right.
Colin Todd, C S Todd & Associates

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
A further thought.  As many will know, as well as being a huge fan of Sir Ken, I am also a huge fan of London Fire Brigade, which I have always regarded as the greatest fire brigade in.......... London. I still remember the day when their head of fire safety policy, one of the true gentlemen of the fire safety world and now a leading fire safety consultant, issued guidance to stop their officers demanding smoke detectors in all hotel bedrooms and advising that heat detectors were fine. To the best of my knowledge, this policy has never been reversed. Further evidence if any is needed that Sir Ken was right.
Colin Todd, C S Todd & Associates