Author Topic: Power Station - Turbine Hall & Boiler House  (Read 5343 times)

Offline Marek

  • Newbie
  • *
  • Posts: 10
Power Station - Turbine Hall & Boiler House
« on: November 09, 2010, 09:15:57 AM »
I am looking at a Turbine Hall (TH) & Boiler House (BH) at a coal fired Power Station that has been in operation for over 35 years.
The building is approx 200 metres x 150 metres with a partition wall that separates the TH and BH, this is not a compartment wall due to its construction and the many openings within.
The BH is has many floor levels, the heighest 55 metres, with associated walkways providing access for maintainance. The floors are metal and of open grill construction; access is via 3 main stairs (1 at either end and 1 centre) that cover all floor levels, plus some interconnecting stairs.
All the stairs are open and it would be very difficult, if not impossible, to enclose them, obviously travel distances are an issue, etc.
The TH is less of a problem as it is an open structure.
My questions are:
1. Under the RRO who are the enforcing authority? Local Fire & Rescue or HSE?
2. This building would, I believe, fall under the category 'Specialist Premises'?
3. The RRO Guide 'Factories and Warehouses' cannot be applied to such premises, are there any other guidelines or documents covering such premises.

Factors that are need to be considered are:-
> High levels of maintainance - strict control on working practices
> Suppression Systems etc. covering Turbines, Mills, Boilers etc.  (with warning alarms)
> Means of raising the alarm and alerting occupants
> History of fires - very few and all localised
> Site has own Fire Station and Response Team
> Chances of building becoming smoke logged is unlikely
> Personnel Working on Site -trained and supervised- task orientated
> Signage, Lighting, FFE
> Dimensions of the building and travel distances available at each working levels are such that there is sufficient room for occupants to move horizontally away from any fire that may occur.

 I think the being  'Reasonable and Practicable in the circumstances of the Case' has to be considered.

Thanks

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Power Station - Turbine Hall & Boiler House
« Reply #1 on: November 09, 2010, 08:34:19 PM »
I would add to your list the details of the persons at risk in the remote areas- numbers and how often, what are they doing whilst up in the gods and if anything went wrong would they be able to escape?

Also what is there to burn and how easy is it to ignite, how quickly would a fire develop, would smoke be a problem?

An RSET/ASET approach is usually  the best way to proceed in these cases.
I generally agree with your points but you will have to ask the site who enforces the Fire Safety Order there. They will have had some past involvement.

Offline Marek

  • Newbie
  • *
  • Posts: 10
Re: Power Station - Turbine Hall & Boiler House
« Reply #2 on: November 10, 2010, 06:54:29 AM »
Thanks Kurnal, as I am usually a follower of the forum rather than a contibutor, your wisdom and advice is always appreciated.

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Power Station - Turbine Hall & Boiler House
« Reply #3 on: November 10, 2010, 10:30:27 AM »
The local FRS is the enforcing authority for the RRFSO, but I would suggest that a huge element of fire safety in that building will be minimising and adapting to what is essentially a process risk, so the FRS should ideally be linking up with the HSE for inspections as the process risks should really be addressed under the HSAWA but there will be some (read: "quite a large") element of grey areas.

For info:
http://www.fia.uk.com/en/Information/Details/index.cfm/obj_id/17A4D106-81F5-451A-989BD32079A5BF07

Offline BCO

  • Jr. Member
  • **
  • Posts: 56
Re: Power Station - Turbine Hall & Boiler House
« Reply #4 on: November 11, 2010, 11:28:57 PM »
There is some decent guidance on fire safety for these types of process/plant buildings in Appendix F of BS 9999. It says pretty much what 5588 used to say for these types of buildings. It recognises the large space, low occupation, massive TDs, mezzanine platforms and ladder access etc.

Offline Marek

  • Newbie
  • *
  • Posts: 10
Re: Power Station - Turbine Hall & Boiler House
« Reply #5 on: November 12, 2010, 10:24:43 AM »
Thanks for the comments and feedback