Author Topic: Maximum area of class F fire (cooking oil) for which extinguishers are suitable  (Read 7857 times)

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Can anyone please shed some light on the fact that according to this table for a fire with surface area of 0.4 m2 you would need 2 x 75F Fire extinguishers.

Have I go this right that a 20 cm x 20 cm surface area which just over A4 paper size you would need to have to hand 2 x 6 ltr wet chem extinguishers to put a fire out.

I am missing the point here I know, but I can't discover why, it seems I need 12 lts of extinguishing medium for a cooking oil fire with a surface are about A4 size.

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287

Have I go this right that a 20 cm x 20 cm surface area which just over A4 paper size

GFSM I think your calculations may have gone a bit awry 0.4m2 is a bit more than 400cm2 more like 4000cm2.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351

Have I go this right that a 20 cm x 20 cm surface area which just over A4 paper size

GFSM I think your calculations may have gone a bit awry 0.4m2 is a bit more than 400cm2 more like 4000cm2.

.4 of a square metre is nearly half of it. So the surface area is around 1M x 1/2M ish which is around half the size of a desk which is around A1 ish size.
Fire ground calcs you understand.
We're not Brazil we're Northern Ireland.

Offline Golden

  • Sr. Member
  • ****
  • Posts: 486
This is where the metres squared and square metres becomes a too complicated for simple minds like mine but as far as I can see from the original post its asking for a fire with a surface area of 0.4m2 - I see that as 40cm x 40 cm?

I obviously don't know about the depth of the tray and contents or if it has been pre-heated but two 6ltr extinguishers doesn't seem excessive - I'd imagine one 6 litres isn't enough and it could be a question that 7 litres would be sufficient rather than the 12 quoted?

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287

I see that as 40cm x 40 cm?

Closer to 63.25 cm X 63.25. I think.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96

Have I go this right that a 20 cm x 20 cm surface area which just over A4 paper size

GFSM I think your calculations may have gone a bit awry 0.4m2 is a bit more than 400cm2 more like 4000cm2.

.4 of a square metre is nearly half of it. So the surface area is around 1M x 1/2M ish which is around half the size of a desk which is around A1 ish size.
Fire ground calcs you understand.

NT, you are truly a genius, as I was having a wierd moment, my brain was stuck in reverse gear for a while, i haven't had to use the simple part of my brain for a long time to calculate something so simple. Thankyou for the kick start with your simple description, I'll have to go and see a doctor next time the cogs get stuck

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351

Have I go this right that a 20 cm x 20 cm surface area which just over A4 paper size

GFSM I think your calculations may have gone a bit awry 0.4m2 is a bit more than 400cm2 more like 4000cm2.

.4 of a square metre is nearly half of it. So the surface area is around 1M x 1/2M ish which is around half the size of a desk which is around A1 ish size.
Fire ground calcs you understand.

NT, you are truly a genius,
I know.
We're not Brazil we're Northern Ireland.

Offline Golden

  • Sr. Member
  • ****
  • Posts: 486
Thanks Tom; I'd read this as 0.4m x 0.4m whereas its (as you rightly point out) 0.4 x 1.0m which is 4000cm2, the square root of 4000 being 63.25. Of course the guidance is written for any shape of container whereas I'd wrongly assumed a square/rectangle so it makes perfect sense now I actually think about it.

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Good Job I asked then

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2493
    • http://www.firewizard.co.uk
For any single risk that calculates as needing more than a single 75F extinguisher other than for travel distance/access issues I would consider that a fixed system is required.

Although if you look at the size of a 75F test tray you would be hard pressed to find a commercial fryer with a single compartment bigger.

Quite a few smaller establishments could suit the various 2 & 3 litre models available, which being cheaper are more likely to be installed, but whilst a lot of companies only push the mega 6 litre version (or don't do F class at all thinking ABC Powder, CO2 or non aspirated AFFF actually work)

This clip shows why powder extinguishers don't really do the business, using a real situation:
http://www.youtube.com/watch?v=X4GPxV_2vV0
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
They say " A picture is worth a thousand words " how true.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.