Author Topic: Info on new extinguisher  (Read 10301 times)

Offline Davo

  • Hero Member
  • *****
  • Posts: 1144
Info on new extinguisher
« on: February 18, 2011, 02:19:08 PM »
Any info on this, please and conformity to BS.


http://s690.photobucket.com/albums/vv266/DavoB/


Manufacturer BWH, Elland- no website


davo

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Info on new extinguisher
« Reply #1 on: February 18, 2011, 04:40:50 PM »
Love the green label.  I doubt it conforms to EN3 but is that a problem if training is provided?

Its one of the new eco friendly foams that are  more bio degradeable and so less harmful to the environnment if released into drains etc.

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Re: Info on new extinguisher
« Reply #2 on: February 18, 2011, 07:44:36 PM »
New one on me, but maybe acceptable because BS 7863:2009 allows between 3 - 5% of the body to be colour coded in accordance with BS 5423 If memory serves.

Anyone confirm more ?
« Last Edit: February 18, 2011, 07:49:02 PM by GFSM »

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2493
    • http://www.firewizard.co.uk
Re: Info on new extinguisher
« Reply #3 on: February 18, 2011, 08:31:46 PM »
You have found an extinguisher from BWH who exclusively manufacture for London Securities, in other words Nu Swift, TVF, MK Fire and many more.

Although Kitemarked it does not technically meet EN3 due to the colour, nor does it meet the UK derivation allowing limited colour coding (implemented in BS 7863)

When they changed the servicing standard BS5306-3 in 2009 there was to be a clause that would result in these extinguishers being condemned as the colouring could confuse a user.

However, the BS5306-3 committee includes manufacturers including London Securities. Because this change would scrap every foam extinguisher installed across the group for the last 5 or 6 years they objected and because a unanimous vote is required to pass a standard it was in limbo for the best part of a year until everyone else backed down and the clause dropped.

The other user of Green labels, TOTAL had accepted the clause, relabelled new versions and produced replacement labels for existing equipment without any objection or fuss.

It's a stored pressure 6 litre biodegradable foam extinguisher with an impressive 27A 183B rating (BWH do a 9 litre water additive with a 43A rating as well!) and will set you back £180 from the MK Fire end of the Group to nearer £300 for the GFA/Nu Swift end
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36