I undertake occupancy assessment of buildings for a customer where they are wanting to occupy buildings upto their maximum capacity having regards for floor space, storey exit, and staircase capacity. I have recently assessed a premises which is provided with a spiral staircase used as a escape stair. Common sense suggests that the occupancy capacity of a spiral staircase should be reduced however I am unable to find any supporting documents.

I would welcome the views of anyone who knows of any guidance confirming how to calculated the occupancy capacity of a spiral staircase.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Occupancy capacity of Spiral Staircases.
« Reply #1 on: March 12, 2011, 10:59:44 PM »
Its a mixture of guidance and common sense. Generally most spirals will only allow a single file of people and they will move a little more slowly than the normal figures given for travel on staircases (7974 if I recall). Top flow rate will be about 30 persons/minute in my opinion. It may not be appropriate to allow for the stacking reservoir effect unless the the staircase is a protected route.
The other issue is that spirals are often accommodation staircases anyway and so not counted for this reason.
Theres a few points made in 9999 about the use of spirals as a means of escape.
« Last Edit: March 12, 2011, 11:01:31 PM by kurnal »

Offline StuartH

  • Newbie
  • *
  • Posts: 43
Re: Occupancy capacity of Spiral Staircases.
« Reply #2 on: March 12, 2011, 11:06:30 PM »
Thanks Alan.

The staircase in question is located in a protected route. Thinking about it these are also fairly frequently found as external escape staircases.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Occupancy capacity of Spiral Staircases.
« Reply #3 on: March 12, 2011, 11:13:11 PM »
Yes thats right, but I think the single file  generally applies unless its a helical rather than a spiral. Nobody likes using one without hanging on to the rail or rope.

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Occupancy capacity of Spiral Staircases.
« Reply #4 on: March 13, 2011, 09:05:16 PM »
Hi,

Just to add slightly to kurnal's comments, it's not generally possible to apply table 7 (table 15 in 9999) to a spiral staircase.  They should be looked upon as governors of flow and not as possessing holding capacity for occupants (table 7 uses this latter principle).  It has been possible, in some cases, to apply table 7 (or table 15) to helical, but not spiral, stairs where those stairs have a large radius and the inner edge of each step has a suitably long tread length.

Stu


Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Re: Occupancy capacity of Spiral Staircases.
« Reply #5 on: March 17, 2011, 07:23:46 PM »
There is a BS for Spirals , it is mentioned in BS 9999 and the wording in the original document is that 2/3rds of the width of the stairs is to be used when assessing moe.  Hope that helps.