Author Topic: Fire evacuation drill for private tenants  (Read 18505 times)

Offline DavyFire

  • Jr. Member
  • **
  • Posts: 55
Fire evacuation drill for private tenants
« on: August 10, 2011, 10:51:39 PM »
Hi all,
City centre development in N. Ireland, 20+ years old, mixed use commercial / residential, courtyard style with no vehicular access.
About 18 shop units - retail / office / cafes etc. Approx 30 private flats mainly 1st floor above the shop units with a few on the ground floor. Most flats have individual access to a raised walkway and down steps to ground level. A few blocks of 3-4 flats using a shared stairs and front door.
The Query!
Landlord wishes to carry out fire evacuation drills for the housing tenants (not the shops and offices) to ensure they evacuate when the fire alarm sounds. What happens if they don't evacuate? Has the landlord any powers, or can the tenants just ignore the fire drill(and the actuation of the fire alarm at other times)
Comments please!
Davy

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Fire evacuation drill for private tenants
« Reply #1 on: August 10, 2011, 11:57:41 PM »
First query would be - does the alarm actually need to extend to the flats based on layout and construction!

If it does then fair enough, but there can be no compulsion for tenants to take part. Depending when it's done most will be out anyway, others won't hear it if it's common areas only & some might even go for one of the sounders with a heavy object!

The fact that most tenants won't respond to a general alarm is one of the cases for compartmentation as first resort, installing a building wide alarm as a last resort.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Fire evacuation drill for private tenants
« Reply #2 on: August 18, 2011, 03:02:21 PM »
When would the landlord carry out the test? Daytime when most will be out? Night time when most will be asleep? Evening time when many will be out, having dinner, watching tv, relaxing, chilling out, etc etc. 
What does he do if nobody leaves?
Is it realistic and is the landlord just ticking a box?
Is it not adequate to provide tenents with written advice?
We're not Brazil we're Northern Ireland.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
Re: Fire evacuation drill for private tenants
« Reply #3 on: August 19, 2011, 11:01:29 PM »
This is why we don't use general alarms in blocks of flats.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire evacuation drill for private tenants
« Reply #4 on: August 20, 2011, 07:14:37 PM »
But sadly, Brian, some , including certain posters, do so.
Colin Todd, C S Todd & Associates

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Fire evacuation drill for private tenants
« Reply #5 on: August 21, 2011, 01:22:39 AM »
It's like hitting your head against a brick wall. Not unsurprisingly the fire alarm people don't like it and I'm constantly sparring with them on firealarmengineers.com

Upset an M&E contractor client who wanted to upgrade alarms in 5 blocks of flats (built to code) and had had the tenants saving up for years only to point out that the systems were not required, some existing stuff should go and instead the money would be better spent on all the smoke vents as everyone on every floor had been inoperative for years, plus the controls were poorly installed in 2, with no manual control on one and the other hurriedly bunged next to the panel in the first floor (using a red MCP no yellow)
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Midland Retty

  • Guest
Re: Fire evacuation drill for private tenants
« Reply #6 on: August 22, 2011, 10:58:22 AM »
Quite a gree. A large RSL / housing provider I've had dealings with is going through a major process of installing communal / common alarm systems in all of their high rise blocks. Not a very good idea at all. It is costing thousands upon thousands of pounds as you can imagine, and will serve no useful purpose at all.

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Fire evacuation drill for private tenants
« Reply #7 on: August 22, 2011, 01:10:25 PM »
Midland, why don't you 'tell' them not to? If you know something is wrong, and you are the enforcing authority, then you should put it right.

Midland Retty

  • Guest
Re: Fire evacuation drill for private tenants
« Reply #8 on: August 22, 2011, 02:17:39 PM »
Enforcing authority?? Not me chummie !!

Although I have explained to them that they should re-consider, and chat with their local friendly fire inspector for further advice / guidance etc etc.
« Last Edit: August 22, 2011, 02:20:15 PM by Midland Fire »

Offline DavyFire

  • Jr. Member
  • **
  • Posts: 55
Re: Fire evacuation drill for private tenants
« Reply #9 on: August 24, 2011, 10:06:23 AM »
Sorry for not replying sooner, been busy, then couldn't logon until Kurnal fixed it for me. Thanks for the comments.
Latest update after a site visit. Originally staff were employed to oversee the complex, check out alarms and call the FS or reset the fire alarm anel. For a few years now due to cutbacks, no staff on duty except the working day. Then it transpires that some of the tenants have keys for the fire alarm panels, go down silence it and go back to bed. There are four panels, one for each block, contained in a locked store to prevent vandalism.
As stated in earlier replies, there is good compartmentation so no need for the shop alarms to sound throughout the premises. I feel it would be built a lot differently today. Unfortunately it has become custom and practice for the tenants to silence the alarms themselves without checking or calling the FS.
The fire alarm engineer supposes if the tenants cannot silence the alarm then it will probably be pulled off the wall in bits. Each flat have their own self contained fire alarm.
Just to make things worse the complex is locked at night to deter intruders. two access gates have EOD's on the inside to allow tenants out, but if a tenant calls a doctor or ambulance they have no access into the complex unless the tenant opens the gate. The FS can cut the lock  for entry. After much debate one gate is left permanently unlocked. Which would be worse, some vandalism, or a doctor unable to reach a heart attack victim?
DavyFire
 

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire evacuation drill for private tenants
« Reply #10 on: August 24, 2011, 08:08:02 PM »
Civvy, there is an ENFORCING AUTHORITY that shall remain nameless, but for the sake of the record shall be referred to a Sest Wussex that has used the powers of enforcement to make people put fire alarm systems into high rise purpose built flats.  Their fire safety officer said it was a requirement of their operational people.  Just remind me, who is running the asylum these days.
Colin Todd, C S Todd & Associates

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: Fire evacuation drill for private tenants
« Reply #11 on: August 24, 2011, 08:35:55 PM »
Oh dear.

There's simply no reply to that. I despair.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire evacuation drill for private tenants
« Reply #12 on: August 26, 2011, 12:16:02 AM »
Civvy, as I sense that deep down you mean well, even though you dont like me,  herewith an invitation to a tour of a high rise block in the area in question, along with sight of the enforcement notices and the notices on the backs of the flat doors required by the fire and rescue authority to tell tenants the evacuation procedures and the location of the assembly point, which had to be reprinted as the F&RS did not like themselves being described as a fire brigade, rather than fire and rescue service.

We can go for fish and chips in paper at the seaside afterwards, skim stones and ponder why I often have a psycopathic dislike of inspecting officers, though the last one I met on site at this place said he agreed that what his colleagues had required was nonsense and he would ask for reconsideration and revert. Alas he retired god knows how long later and never did revert. It didnt matter as the system was already in, having cost some tens of thousands of pounds and as Tony said, keeping the fire alarm industry bouyant.
« Last Edit: August 26, 2011, 12:18:01 AM by colin todd »
Colin Todd, C S Todd & Associates

Offline SamFIRT

  • Sr. Member
  • ****
  • Posts: 382
  • Looking for the truth
Re: Fire evacuation drill for private tenants
« Reply #13 on: August 26, 2011, 08:41:04 AM »
Quote
as the F&RS did not like themselves being described as a fire brigade, rather than fire and rescue service.

Would it be correct to call Open reach the GPO? Or Network Rail Southern railways, or LMS? Or a CD an LP? Or call an e mail a telegram and have it delivered by a 16 year old on a BSA bantam?   ;)

The Government (the previous one) enforced the change nationally from "Brigade" to Fire and Rescue Service, against the will of many; but it is here……….. move with the times ………………….especially related to legal documentation.
 
This constant negativity towards Fire and Rescue Services is boring.  ::)
« Last Edit: August 26, 2011, 08:42:52 AM by SamFIRT »
Sam

Offline BLEVE

  • Sr. Member
  • ****
  • Posts: 324
Re: Fire evacuation drill for private tenants
« Reply #14 on: August 26, 2011, 06:46:51 PM »
Civvy, as I sense that deep down you mean well, even though you dont like me,

Shock  :o there are others out there that dont lick your boots?, what a surprise ;D