Author Topic: sprinkler linked to a fire alarm  (Read 7154 times)

Offline longjohn

  • Jr. Member
  • **
  • Posts: 71
sprinkler linked to a fire alarm
« on: November 29, 2011, 09:34:35 AM »
Hi, Can anyone assist. If a (not to full spec) sprinkler system is installed and it is linked to the premises fire alarm system does it still need to have its own alarm bell. The system is very old but is serviced and tested to current standards (maintenance, not design and installation of course). I feel that from a risk assessment point of view if it works and it also raises and alarm it is better than not having a system at all. Basically the bell is knackered and needs replacing but does it have to! My question may be irrelevant if the insurers insist on it anyway, but I thought I would ask your esteemed views 

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2493
    • http://www.firewizard.co.uk
Re: sprinkler linked to a fire alarm
« Reply #1 on: November 29, 2011, 07:52:31 PM »
Personally if a system is retained, even if it is to an older standard, I would expect it to be fully working, so if it has a water motor gong then that should still function. Traditionally I would have thought one of it's purposes is to warn passers by of a fire out of hours hence their installation on outside walls, although if the building fire alarm is monitored it could serve the same purpose (more effectively).

One caution with old systems is not to over-rely on them as much and to ensure tenants don't in FRAs as often the premises bear little resemblance in layout and risk to the original use and the systems are not always resurveyed and re-engineered appropriately to suit this. Also few users have service staff carry out a full audit as per the BS and service visits early venture outside the valve chamber, missing the numerous blocked, painted and poorly positioned heads around the site.

That and water supply issues mean that there is a greater chance of the system failing to contain a fire and care needs to be taken on how much weight you give to the presence of a system.

Most of the old systems from the big former single occupier industrial premises that date from the 1900-1970's period simply get drained as users won't pay for upkeep & re-engineering if there is no absolute requirement to maintain them, which as most were for property not life is often the case & insurers don't seem bothered about their removal for normal risks, so it's refreshing to hear of a site that is retaining them.

Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline longjohn

  • Jr. Member
  • **
  • Posts: 71
Re: sprinkler linked to a fire alarm
« Reply #2 on: December 12, 2011, 11:25:41 AM »
Many thanks for that. They do have a very competent on site engineer, the system isn't relied upon at all from a life safety point of view. It was a 'passers by' warning originally but now they have 24/7 on site security and a full AFD system so that is no longer an issue. Thanks for your input.