will this extract from the British Standard help? appreciate this may be a temporary measure but guidance is given on stair minimum width when in use.
[b]BS 8300:2009+A1:2010Design of buildings and their approaches to meet the needs of disabled people –
Code of practice
8.3.6 Stairlifts
Stairlifts should not be installed in new buildings. Stairlifts for existing buildings should only be installed where it is not possible to install a conventional passenger lift or a vertical lifting platform.
NOTE 1 Prior to the installation of a stairlift in a public building, the building control authority and the fire authority should be consulted to ensure that means of escape are not compromised.
Stairlifts, whether for seated, standing or wheelchair users, should conform to ISO 9386-2.
NOTE 2 BS 5776:1996, Annex A gives information on the use of stairlifts in buildings other than dwellings. A European standard for stairlifts, pr EN 81-40, is in preparation.
Chair stairlifts should only be installed where it is not practical to install a wheelchair stairlift.
NOTE 3 Chair stairlifts might not be suitable for many people with impaired mobility. On the other hand, wheelchair stairlifts with lowering guard rails or flip-up seats do not suit all people who have difficulty walking.
NOTE 4 Where, in an existing building, a stairlift is required for a known person, e.g. a member of staff, the type of stairlift needs to be chosen to suit their particular needs.
Stairlifts for public buildings should ideally be located in sight of a receptionist or another member of staff in case users get into difficulty, and should be fitted with an alarm that conforms to the requirements of ISO 9386-2.
The controls of a stairlift should be designed to prevent unauthorized use (see ISO 9386-2).
For a building with a single stairway, the clear stairway width for means of escape should be maintained between the carriage rail of the stairlift and the handrail opposite.
For a building with two or more stairways between storeys, a stairlift should only be installed on a stairway that is not intended to be used as a means of escape.
When in a parked position, a stairlift should not obstruct the required clear width of a stairway, or cause a potential hazard for blind and partially sighted people using the stairway or the adjoining landings.
There should be a minimum clear width of 600 mm between the folded down platform of a wheelchair stairlift and the handrail opposite.
NOTE 5 In some buildings, the requirements for means of escape given in the Building Regulations 2000, Approved Document B [16] and its equivalents in Scotland [17] and Northern Ireland [18] might demand a greater minimum clear width.