Author Topic: Fire doors without smoke seals  (Read 18664 times)

Offline lingmoor

  • Sr. Member
  • ****
  • Posts: 264
Fire doors without smoke seals
« on: September 18, 2012, 10:36:06 AM »
In what situation would you accept fire doors that are already insitu but do not have cold smoke seals/intumescent strips?

I have come across this with two admin offices on the first floor and a patient clinic on the ground floor with a single protected staircase...there's two way travel on ground floor

personally I would risk assess it as ok because with the fire alarm system installed they would all have early warning and get out

however, I'm  unsure if local enforcement officers would see it that way!

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Fire doors without smoke seals
« Reply #1 on: September 18, 2012, 12:09:04 PM »
In what situation would you accept fire doors that are already insitu but do not have cold smoke seals/intumescent strips?

I have come across this with two admin offices on the first floor and a patient clinic on the ground floor with a single protected staircase...there's two way travel on ground floor

personally I would risk assess it as ok because with the fire alarm system installed they would all have early warning and get out

however, I'm  unsure if local enforcement officers would see it that way!
It depends on your local enforcement officer Lingmoor but you have made an assessment already by considering them ok on the bases of the compensatory detection system. Unless enclosing a stairway I would suggest them ok with the detection installed and if the enforcement authority didn't agree, it is easily remedied.
That's my view which may not be that of the EA.
We're not Brazil we're Northern Ireland.

Offline lingmoor

  • Sr. Member
  • ****
  • Posts: 264
Re: Fire doors without smoke seals
« Reply #2 on: September 18, 2012, 12:18:58 PM »
thanks for your opinion nearlythere


Midland Retty

  • Guest
Re: Fire doors without smoke seals
« Reply #3 on: September 18, 2012, 12:46:54 PM »
I would agree with NT. If you can justify why you have done something your friendly local fire officer should (hopefully) be able  to follow your reasoning and go along with it.

Latest standards would dictate you need strips and seals on your door but with existing doors, even doors enclosing a single staircase, you may not need to upgrade to strips and seals.

It would be be different if it was a sleeping risk but in the situation you describe if people are awake and alert, you have early warning, and trained staff to marshall visitors out the building quickly, and they can reach a final exit well before fire could effect the staircase or MOE, then why do you need to upgrade the doors? That would be my logic. 

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: Fire doors without smoke seals
« Reply #4 on: September 18, 2012, 12:50:27 PM »

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Fire doors without smoke seals
« Reply #5 on: September 18, 2012, 05:35:44 PM »
if you havent read this - then you probably should

http://www.info4fire.com/news-content/full/hotel-bedroom-fire-door-determination

Yes but the determination was not issued as general guidance.

The determination is based entirely on the circumstances of the hotel in question, and the decision was taken after careful consideration of the particular circumstances of the case.

I get your drift WB but I still generally go for Int and SS on doors to stairways in sleeping risks.
We're not Brazil we're Northern Ireland.

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: Fire doors without smoke seals
« Reply #6 on: September 18, 2012, 10:56:20 PM »
I was going to bring up wee brian's point but was beaten to it.  I can't see how the EA could issue a notice to get strips and seals fitted in this case; it was hard enough in the hotel in question.

I think the new flats guide (published last year) brought some common sense to the issue of strips and seals.  If the doors are the original FD30/60 doors and still perform their function i.e. they have effective self closers and are not breached or damaged they are fine as they are.  If a door no longer performs its function or is damaged then it should be replaced with a new FD30s door to current standards.  I think when the Fire Safety Order first came in fire officers went mad enforcing strips and seals on any door in any building that didn’t have them.  Time has now moved on and hopefully a more realistic, risk based approach is being accepted where a fire risk assessment has been done and the omission of strips and seals is noted, risk assessed and justified.

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: Fire doors without smoke seals
« Reply #7 on: September 20, 2012, 01:14:00 PM »
See...

http://fire.org.uk/forum/index.php?topic=5782.msg63430#msg63430

All the guidance available says they should be installed in F/R doors & explains why. 

Now... you don't have to follow the guidance of course (that's why it's called "guidance"), but if you don't you should be able to explain why you can achieve an equivalent level of safety without upgrading the doors.  This might be perfectly possible, based on the circumstances (considering means of detection & warning; means of escape; fire-fighting access etc, etc...).  The determination cited a good example - smoke detection was installed in the rooms, which arguably compensated for the uncertain fire resistance performance of the doors.

 

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: Fire doors without smoke seals
« Reply #8 on: September 20, 2012, 09:25:12 PM »


All the guidance available says they should be installed in F/R doors & explains why. 


 

Hi Fishy, which guidance are you referring to that recommends the fitting of S&S to good fitting, non damaged existing fire doors?  There is also the problem of removing a decent door, rebating the door or frame to install S&S and the door it not as good fit in the frame as before.  If they are needed and are justified I have no problem, I was meaning that we should by now have moved away from "all doors need S&S" mentality regardless.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: Fire doors without smoke seals
« Reply #9 on: September 21, 2012, 09:12:44 AM »
What the Det was trying to say was that you shouldnt just impose the latest 'new build' standards on exisiting buildings unless the risk justifies an upgrade.

The same guidance that says strips and seals on fire doors will also ask for a whole bunch of other things that you won't find in some existing buildings. Do we knock down every building in the country and start again?

Clearly, the Det is not formal guidance, but why do you think they get published?

Offline Golden

  • Sr. Member
  • ****
  • Posts: 486
Re: Fire doors without smoke seals
« Reply #10 on: September 21, 2012, 09:34:35 AM »
I believe the determination quite clearly says that the doors should have strips and seals; what it confirms is that this may not necessarily be a 'priority' requiring immediate remedial works when there are other features within the premises that compensate. One of the fundamental issues within the determination is that the risk assessment must clearly state on what grounds that the lack of strips/seals or other fire (protection) measures is considered acceptable and for how long - i.e. does the RP have a programme to replace these doors over a set period of time.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire doors without smoke seals
« Reply #11 on: September 21, 2012, 10:42:01 AM »
Golden, the determination does not say anything of the sort.  Huge amounts of ratepayers money was wasted by this fire and rescue authority because of an old fashioned prescriptive approach to the provision of fire precautions without any proper consideration of risk versus cost.  There is no suggestion that the doors need to be fitted with strips and seals. Read what Wee B and Willie said and listen to what they say.
Colin Todd, C S Todd & Associates

Offline Golden

  • Sr. Member
  • ****
  • Posts: 486
Re: Fire doors without smoke seals
« Reply #12 on: September 21, 2012, 11:05:01 AM »
Colin, I was trying to state a case that the determination does not say that strips/seals are not required and writing 'the doors' in my response was inaccurate and I apologise if anyone is mislead. From my reading of the determination fire doors generally should be fitted with strips and seals but in certain circumstances these may not be necessary if the provision of such does not reduce the risk to such an extent that justifies the costs; particularly where other fire precautions are present that compensate for the lack of strips/seals.

The point I was trying to make is that some interpret the determination to mean that strips and seals are not required whereas this needs to be considered on a case by case basis rather than a generalisation. I think what I was trying to say was exactly what you've said in your second sentence - that being prescriptive 'either way' can lead to confusion and that proper consideration of the bigger picture is necessary.

Edit: And I fully agree with Wee B and Willie and wasn't trying to argue against them, I am however concerned that there are others out there without their FS backgrounds that will interpret the determination in a way that suits them!
« Last Edit: September 21, 2012, 11:16:05 AM by Golden »

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: Fire doors without smoke seals
« Reply #13 on: September 21, 2012, 02:12:04 PM »
If we look at it from another angle for a moment.  Let’s say a new fire door standard comes out in 2013 (I don’t think one does by the way?) and this new BS determines due to some new fire door tests and research that all hinges on NEW fire doors need to be rated to 1200oC, whereas before around 800oC was fine.  On an FRA of an existing building would you recommend that all the hinges on all fire doors are replaced for 1200oC rated ones irrespective of if there are compensations in place?  Or would you say replace them on a “programmed plan of refurbishment works”.  For what its worth, I’ll give you my view……both would be wrong.  However if any door was replaced due to damage etc then it would be replaced with an FD30s1200 door. (I made that bit up please don’t Google it).

The point I am making is sometimes what is existing is just that existing and acceptable as it is….. if it can be justified, risk assessed and documented appropriately in the FRA.

Offline Golden

  • Sr. Member
  • ****
  • Posts: 486
Re: Fire doors without smoke seals
« Reply #14 on: September 21, 2012, 02:58:37 PM »
They would  have to redefine the time temperature curve first as it only goes up to 800oC up to 30 minutes so I would question where they got their evidence from!

Of course I would ignore that in existing buildings and not due to cost but due to the fact that I would consider the risk of a hinge failing above that temperature is insignificant - for FRA purposes at least - as I may well ignore brass hinges and many other minor infringements of the current standards if I didn't consider it to be risk critical. However some doors do  need replacing or upgrading with respect to IS/SS as the positive pressure test indicates that smoke and hot gases may pass around the door and that his can happen quite quickly.

I am 100% behind not trying to bring all buildings up to new build standards and I find the issue of fire doors (nominal or BS certified) to be one of the most interesting discussion points - and we haven't even mentioned door frames yet. For me its all about context and not sweeping generalisations that because a determination has been made for a specific case that this now becomes the new rule to be applied in all circumstances.