Author Topic: Ohh no not again - green box's  (Read 25398 times)

Offline lingmoor

  • Sr. Member
  • ****
  • Posts: 264
Re: Ohh no not again - green box's
« Reply #15 on: December 19, 2012, 02:49:10 PM »
so are people saying that if it opens on actuation of fire alarm, fails safe to open in the event of power failure, there's a double pole red call point next to the fire exit door(so if the fire alarm fails it will still open)...it still needs a green box?

I wouldn't ask for it

edit...maybe I read the op's question wrong
« Last Edit: December 19, 2012, 02:51:06 PM by lingmoor »

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Ohh no not again - green box's
« Reply #16 on: December 19, 2012, 04:30:55 PM »
so are people saying that if it opens on actuation of fire alarm, fails safe to open in the event of power failure, there's a double pole red call point next to the fire exit door(so if the fire alarm fails it will still open)...it still needs a green box?

I wouldn't ask for it

edit...maybe I read the op's question wrong

Lingmoor, in a typical set-up, the operation of a fire alarm call point sends a signal back to the fire alarm control panel, the fire alarm control panel then sends a signal back to a relay which disconnects the power to a electromagnetic door lock causing the door lock to release. None of this is fail-safe, and can't easily be made fail-safe. the typical fire alarm call point has no direct interconnection with the electromagnetic door lock.

If you rely purely on the operation of the fire alarm system to release a locked door then you have a set-up with many potential failure points and no way of releasing the door in an emergency if the set-up does fail.

A correctly installed EDR switch (green box) is about as good as you can get in providing a system where you can always effect escape through an electromagnetically locked door (fitted with fail-safe lock).

Offline lingmoor

  • Sr. Member
  • ****
  • Posts: 264
Re: Ohh no not again - green box's
« Reply #17 on: December 21, 2012, 04:08:44 PM »
Wiz

yes I mis-read the OP's post

I was talking about double pole fire alarm call points that have a direct connection with the electromagnet..same as a green box

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Ohh no not again - green box's
« Reply #18 on: December 21, 2012, 04:38:05 PM »
Wiz

yes I mis-read the OP's post

I was talking about double pole fire alarm call points that have a direct connection with the electromagnet..same as a green box


In my 30+ years in the business, I have not seen an installation using a fire alarm call point as also an Emergency Door Release switch. It sounds like it might be a good idea although the BS don't recognise such a set up. The switching of the the electromagnetic door lock would have to be double-pole to suit current BS, so that means the 'combined' switch would have to be triple-pole (at least) to also accommodate the signalling to the fire alarm system. And I wonder if there would be any confusion regarding people expecting to see a 'green box' EDR and only finding a fire alarm mcp?



Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Ohh no not again - green box's
« Reply #19 on: October 21, 2013, 09:22:15 AM »
Morning all and a great weekend for Irish rugby it has been. 100% success rate for the four provinces.

Anyway, following a comment in an engineers report that the operation of a green box should actuate the fire warning system I have looked through BS7273 Pt4 and take from what I have read, or not read, what I have always assumed, that this is not the case.

Am I still correct?
We're not Brazil we're Northern Ireland.

Offline Paul2886

  • Full Member
  • ***
  • Posts: 178
Re: Ohh no not again - green box's
« Reply #20 on: October 21, 2013, 10:25:06 AM »
You are right. Have never heard of an green EDR activating the fire alarm system. Ask him where he accessed his information.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Ohh no not again - green box's
« Reply #21 on: October 21, 2013, 10:47:14 AM »
You are right. Have never heard of an green EDR activating the fire alarm system. Ask him where he accessed his information.
Knowing the outfit who reported it Paul I would think his information came from up the U bend. This "Registered" outfit wired a fire alarm system with flat T&E.
We're not Brazil we're Northern Ireland.

Offline Paul2886

  • Full Member
  • ***
  • Posts: 178
Re: Ohh no not again - green box's
« Reply #22 on: October 21, 2013, 03:41:58 PM »
Well there you are NT....say no more

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2493
    • http://www.firewizard.co.uk
Re: Ohh no not again - green box's
« Reply #23 on: October 21, 2013, 08:17:19 PM »
It's an emergency door release not a fire door release, you might need to use the exit when sounding the alarm is not required or even counter productive - perhaps they were getting mixed up and meant that a fire warning system should release the door.


They will be saying next that a fire alarm break glass should set off all the sprinklers (because that's what happens on TV....) ;D
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: Ohh no not again - green box's
« Reply #24 on: October 21, 2013, 08:53:53 PM »
perhaps they were getting mixed up and meant that a fire warning system should release the door.
No. It was the green box.
We're not Brazil we're Northern Ireland.