I have been exploring AD B and the requirement for fire compartmentation in buildings of three storeys converted to flats.
In general, purpose built blocks of flats are constructed with 60 minutes fire resisting compartmentation to facilitate the stay put approach in the event of a fire. Table A2 points back to para 7.9 and 7.10 which allow for 30 minutes fire resistance for converted buildings having no more than three storeys. There is no indication in the paragraph of a need for a fire alarm system to compensate for the reduced level of fire resistance, and discussions with a local building control officer have confirmed that no further compensation would be required.
The difficulty that this raises in my mind is in relation to the principle of the stay put procedure, which appears to be founded in the 60 minute separation, and the suggestion that those on the second floor of a converted building will be ok to stay put with only 30 minutes separation.
I note that this option for reducing FR in converted flats is omitted in BS 9991.
I would tend towards seeking 60 minutes FR even in flat conversions where possible, using BRE Digest 208 to upgrade the floors where necessary. I would welcome your thoughts on this one - particularly those who are aware of the founding principles or rational that led to the writing of these two paragraphs - so that I can better understand why this reduction is acceptable in conversions when it is clearly not acceptable in new-build.
Thank you.
Paul