Author Topic: ice making machine  (Read 4503 times)

Offline lingmoor

  • Sr. Member
  • ****
  • Posts: 264
ice making machine
« on: July 11, 2013, 10:46:48 AM »
Hi all

An incident recently occured in a hospital where an ice making machine caught fire. The fire service has said that this was due to the water to it being turned off and the power left on. There was no thermostat cut off mechanism to this machine.

The machine had a heating element and this element apparently is there to form ice cubes from the  sheet ice that is formed initially, the cubes then drop into a container.

The external service engineer is saying that the water was on, but on investigation by the estates fitter it appears that the fire service were right and that the water supply was off and it needs a spanner to do this so no ward staff would have turned it off
The machine was serviced the day before the fire.

has anyone else had experience of this type of incident?

Cheers.
« Last Edit: July 11, 2013, 10:48:28 AM by lingmoor »

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: ice making machine
« Reply #1 on: July 11, 2013, 06:53:26 PM »
No, but if it stops the English from pouring gallons of water into finest single malt whisky I am all for the destruction of the machines.
Colin Todd, C S Todd & Associates

Offline SamFIRT

  • Sr. Member
  • ****
  • Posts: 382
  • Looking for the truth
Re: ice making machine
« Reply #2 on: July 12, 2013, 07:39:30 AM »

Interestingly refrigeration devices these days use LPG as a refrigerant gas (propane or iso-butane are popular) and the insulation may well be blown with cyclo-pentane so will burn well or cause explosions.  :o

Sam