Flow rate for hosereels
« on: October 24, 2013, 12:42:27 PM »
Whats the flow rate for Hosereels these days? EN 671-1:2012 is no help

Offline Dinnertime Dave

  • Hero Member
  • *****
  • Posts: 819
Re: Flow rate for hosereels
« Reply #1 on: October 24, 2013, 08:22:31 PM »
Not a definitive answer but an example

http://www.aespl.com.sg/pdf/FIXED%20TYPE%20HOSEREEL.pdf

« Last Edit: October 24, 2013, 08:24:17 PM by Dinnertime Dave »

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2493
    • http://www.firewizard.co.uk
Re: Flow rate for hosereels
« Reply #2 on: October 24, 2013, 10:53:02 PM »
30 litres a minute was what was in the old BS5306-1 and as far as I recall that flow rate is still what reels should be tested to when serviced although its quite a while since I've serviced any as they are less and less common these days.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: Flow rate for hosereels
« Reply #3 on: October 25, 2013, 10:45:07 PM »
thanks guys

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Flow rate for hosereels
« Reply #4 on: October 29, 2013, 11:22:58 PM »
Brian, try the previous version of 671-1.
Colin Todd, C S Todd & Associates

Offline lancsfirepro

  • Full Member
  • ***
  • Posts: 175
Re: Flow rate for hosereels
« Reply #5 on: October 30, 2013, 09:23:21 AM »
BS 5306-1 refers you to EN671-3 for maintenance.  Unfortunately, EN671-3 (2009 version at least) does not give you any flow rates or throw ranges; only that "the flow of water is steady and sufficient".  As Colin suggests, EN671-1 will give you type testing information.  See below.





I would suggest that the very fact that this information is not detailed in the standard that covers the maintenance of hose reels that the actual flow rate is not that critical.  I'd be happy to go off my own determination of what I considered to be a steady and sufficient flow of water when I rinse the van down in the car park!  ;)

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2425
Re: Flow rate for hosereels
« Reply #6 on: October 31, 2013, 01:48:06 PM »
thanks all - very helpful