Gentlemen, the following is taken from Williams third post on this topic.
44.2 Recommendations for weekly testing by the user
When testing the fire detection and fire alarm system, there may be a need to isolate ancillary outputs.
The following recommendations apply.
a) Every week, a manual call point should be operated during normal working hours. It should be confirmed that the control equipment is capable of processing a fire alarm signal and providing an output to fire alarm sounders, and to ensure that the fire alarm signal is correctly received at any alarm receiving centre to which fire alarm signals are transmitted. It is not necessary to confirm that all fire alarm sounder circuits operate correctly at the time of this test.
Could somebody please explain what this last sentence actually means to somebody that doesn't do alarms but is involved on the periphery of a dispute over whether the sounders can be turned off during a call point test. We've already established that it isn't purely a test of the little red box on the wall.
Thanks.
John