Author Topic: Call point testing in flats  (Read 29572 times)

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Call point testing in flats
« Reply #30 on: July 03, 2014, 11:46:01 AM »
The counter to the reverse alarp argument can be,  in many cases,  "if I built this today what would the current design benchmarks say I need to install to create an acceptable level of safety"?

Offline hammer1

  • New Member
  • Full Member
  • *
  • Posts: 157
Re: Call point testing in flats
« Reply #31 on: November 17, 2014, 09:23:14 AM »
Daily checks were dropped from BS 5266-1 years ago.

Are they still not in BS5266 Part 8? in regards to a visual inspection?.

Offline TFEM

  • Full Member
  • ***
  • Posts: 121
Re: Call point testing in flats
« Reply #32 on: November 20, 2014, 10:29:36 AM »
Gentlemen, the following is taken from Williams third post on this topic.

44.2 Recommendations for weekly testing by the user

When testing the fire detection and fire alarm system, there may be a need to isolate ancillary outputs.

The following recommendations apply.
a) Every week, a manual call point should be operated during normal working hours. It should be confirmed that the control equipment is capable of processing a fire alarm signal and providing an output to fire alarm sounders, and to ensure that the fire alarm signal is correctly received at any alarm receiving centre to which fire alarm signals are transmitted. It is not necessary to confirm that all fire alarm sounder circuits operate correctly at the time of this test.


Could somebody please explain what this last sentence actually means to somebody that doesn't do alarms but is involved on the periphery of a dispute over whether the sounders can be turned off during a call point test. We've already established that it isn't purely a test of the little red box on the wall.

Thanks.

John

Offline Graeme

  • Newbie
  • *
  • Posts: 20
  • Worked on fire alarms since 91 and still learning
Re: Call point testing in flats
« Reply #33 on: November 20, 2014, 10:56:47 AM »
basically that means if you test the break glass unit -then you should hear the sounders going and if connected to a remote monitoring centre, they have received the fire signal.

you are not expected to run round the building and confirm that all the sounders are working.

and test the system through the day.
Bafe SP203-1 Technical - Sales Engineer

Design , programming and fault finding.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Call point testing in flats
« Reply #34 on: November 20, 2014, 09:09:21 PM »
The live sounder testing element of the weekly test rises in importance where site make their service firms do silent service visits - if you didn't check the sounders weekly they would never get tested in many buildings.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline TFEM

  • Full Member
  • ***
  • Posts: 121
Re: Call point testing in flats
« Reply #35 on: November 21, 2014, 08:02:19 AM »
Thanks......so would I be right in saying that the sounders in the circuit/zone that the tested call point is on should be audible thereby confirming that the alarm system is operating correctly?

Sounders in other zones can be silenced for the duration of that specific call point test?

John

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: Call point testing in flats
« Reply #36 on: November 21, 2014, 09:29:33 AM »
No, all the sounders should sound to show that the entire system is working correctly.

The usual practice is to test the fire alarm at a set day and time every week. Hopefully if the alarm does not sound in another area of the building someone will come up to you and ask you why the fire alarm test didn't happen, which would indicate a fault. The purpose of using a different call point each test is to check that every zone is working on a rotating basis.

Generally fire alarm systems are very robust and do not go wrong that often so this procedure is adequate.

Obviously if there is a zoned fire evacuation system in place and the fire alarm will only go off in certain areas, each zone of the evacuation system needs to be teste4d weekly.
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Call point testing in flats
« Reply #37 on: November 21, 2014, 01:11:24 PM »
The other purpose of the weekly test is to demonstrate the sound of the alarm to the staff. Silent mode is not quite so effective in this regard. ;)

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Call point testing in flats
« Reply #38 on: November 22, 2014, 06:53:48 PM »

Quote
Daily checks were dropped from BS 5266-1 years ago.
Are they still not in BS5266 Part 8? in regards to a visual inspection?.
Quote


No Hammy, they are not. Only a check of the visual indicator on a CB PSU, which are far from common.

TFEM, All that is necessary is to operate a single call point, and check that the CIE is not dead by hearing alarms sounding.  As someone said, you hope that people will tell you if the alarm is not adequately audible in their area.

 
 
 
Colin Todd, C S Todd & Associates

Offline TFEM

  • Full Member
  • ***
  • Posts: 121
Re: Call point testing in flats
« Reply #39 on: November 30, 2014, 07:06:50 PM »
Thanks for your help gentlemen.

The guy that was annoyed by a tinkling bell once a week has instructed the responsible person to carry on as before following advice from their fire risk assessor, fire alarm company,  your comments on the forum, uncle Tom Cobbly and the realisation that he can't win.

John