Author Topic: Staff Accomodation  (Read 3636 times)

Offline stevew

  • Full Member
  • ***
  • Posts: 149
    • http://firesureuk.co.ok
Staff Accomodation
« on: May 05, 2015, 08:59:52 PM »
Large private estate with accomodation provided with employment.
Two flats within building used for other purposes.

Remaining areas within the building are either private or come under the RRO.
Fire in these areas may impact on the safety of flat occupants.

Do the flats come under the RRO?
Or does it stop, as with the general definition of flats, at the entrance door.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Staff Accomodation
« Reply #1 on: May 05, 2015, 10:33:43 PM »
The flats internally are domestic premises and inside the front door is not subject to the RRO. However the occupiers of the flats are relevant persons who could be affected by a fire in other parts of the building or in any communal areas and so the FRA of the remainder of the building must take them into account.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Staff Accomodation
« Reply #2 on: May 07, 2015, 09:08:26 PM »
You sure you have enough information to say that, Big Al.
Colin Todd, C S Todd & Associates

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Staff Accomodation
« Reply #3 on: May 07, 2015, 09:46:39 PM »
I think so Colin from the op. What have I overlooked?