Hi David and Kurnal,
I've just had a look at 12101 part 10 - 2005 'Power Supplies' and have copied some relevant sections below - sorry I haven't got time to go through it in detail but a bit busy at the moment!!
If a smoke and heat control system fails to the fire operational position on loss of power, only one power source shall be required. For non-fail safe smoke and heat control systems there shall be at least two power
sources: the primary power source and the secondary power source. The primary power source shall be designed to operate from the public electricity supply or an equivalent system. The secondary power source,
for example batteries or a generator, shall be permanently available, tested and maintained.
Each power source, on its own, shall be capable of operating those parts of the smoke and heat control system for which it is intended.
If the primary power source fails, then the p.s.e. shall be automatically switched over to a secondary power source. When the primary power source is restored, the p.s.e. shall be automatically switched back.
If the switching from one power source to the other causes an interruption in supply of power, the duration of the interruption shall be specified in the manufacturer?s data (see Clause 9).
Where there are two or more power sources, failure of one of the power sources shall not cause the failure of any other power source or the failure of the supply of power to the system.
The secondary power source may also be used for other functions, e.g. day to day comfort ventilation. When used in this way the p.s.e. shall ensure that sufficient power is retained for emergency use as specified in
Clause 6, e.g. by preventing further use for the other functions.
6.2.2 At the end of the maximum standby period supplying the maximum standby current Imax a the battery shall be capable of supplying the maximum short duration current Imax b for a period of 180 s with the output voltage within the range specified by the manufacturer.
NOTE 1 To allow for possible failures of equipment or of the incoming mains supply, the secondary supply should be capable of maintaining the system in operation for at least 72 h, unless provision is made for immediate notification of failure, either by local or remote supervision of the system, and a repair contract is in force giving a maximum repair period of less than 24 h. In this case the minimum standby capacity may be reduced from 72 h to 30 h or may be further reduced to 4 h if spares, repair personnel and a standby generator are available on site at all times.
The actuation of the vents is covered in AD B para 2.26 which states "In single stair buildings the smoke vents on the fire floor and at the head of the stair should be actuated by means of smoke detectors in the
common access space providing access to the flats. In buildings with more than one stair the smoke vents may be actuated manually (and accordingly smoke detection is not required for ventilation purposes). However, where manual actuation is used, the control system should be designed to ensure that the vent at the head of the stair will be opened either before, or at the same time, as the vent on the fire floor."
Hope this helps.