Which document tells me about battery standby, cable specifications etc
Which document tells me about the system operation ie. should only the fire floor AOV open or can others open as a fire progresses ?
It appears that on your first question most of the information you require should be found in BS EN 12101-10:2005 Power Supplies.
On your second question I can only find it in the colt and feta guidance which is not very detailed, I think you would be better looking at the reasons why.
The first possibility is any vents open above the fire could smoke log the lobbies, this would depend on the level of the neutral plane.
The second possibility is, in a fire situation the vent shaft is acting as a chimney and any additional air entering the shaft reduce the chimney updraft therefore the effectiveness of the fire venting system. This could be the reason why all the vents should be closed except the floor on fire and the staircase vent.
Considering the principle of multi storey flats, each floor should be compartmented by 60 min separation and the FRS be in attendance within that time, who will take over the manual control of the fire venting system.
My thoughts for what they are worth - dive in the slit trench and put my tin hat on.