Author Topic: Compartmentation of roof voids above self contained flats  (Read 45016 times)

Offline Seetek

  • Newbie
  • *
  • Posts: 24
Re: Compartmentation of roof voids above self contained flats
« Reply #45 on: August 27, 2019, 05:05:24 PM »
Just to pick this up again.

Would you consider that any form of retrospective cavity barrier is required if the floor within an open communal roof void is a concrete slab?

Obviously there is potential for fire spread across the open void but little chance of ingress into the flats.

I would think cavity barriers would be needed as per ADB in this case. A similar scenario is discussed in the specialised housing guide, although different premises, the same principle would apply IMO.

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: Compartmentation of roof voids above self contained flats
« Reply #46 on: August 28, 2019, 10:06:37 AM »
...Systems are now available in which ceilings and floors can be upgraded to provide an hours FR from above and below and meet BS 476;pt 21 criteria...

We'd be very interested in these (do tell who offers them)... British Gypsum used to do a variation of their 'MF' ceiling but they're reluctant to offer formal evidence of fire performance for it these days.  I also thought you couldn't test a ceiling/floor from above to below under BS 476: Part 21 (only under the EN standards), but I'd be quite prepared to be proven wrong.

I wouldn't use it for resi, but we do have situations in non-domestic premises where corridor walls haven't been built up to the soffit (depressingly common) where it might be useful.

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: Compartmentation of roof voids above self contained flats
« Reply #47 on: October 01, 2019, 02:56:15 PM »
You also need to consider the risk of a fire breaking out of a window, affecting the eves and getting into the roof that way. Also external fire on the roof due to hot works etc.