Clause 12.2 Commentary
"Where a Category L1, L2, L3, L4 system is not present, detectors will need to be installed specifically to initiate release of the doors; such a system is, by definition, a Category L5 system."
12.2.2 In buildings with a Category L1, L2 or L3 system, the selection, provision and siting of automatic fire detectors are deemed to be satisfactory for compliance with this part of BS 7273. In all other cases, a Category M/L5 system conforming with 12.2.3 to 12.2.7 should be provided or in the case of a Category L4 system the provision and siting of automatic fire detectors should conform to 12.2.3 to 12.2.7 in those parts of the escape routes in which electrically held-open doors are provided.
I'm still a little confused ........ surely it still needs L5 minimum ?