Thanks Bill, I was asked does a twin wire fire alarm conform to the BS 5839 in relation to clause 12.2.2 especially (j) which says "In the event of a single open circuit or short circuit fault on any circuit that serves the fire alarm sounders, at least on single fire alarm sounder, normally located in the vicinity of the CIE, should still sound correctly if a fire alarm condition occurs anywhere within the building."
I was a former artist in burnt clay not a sparky so I told him I could not help him, but I am interested and would like to find an answer.
The way I read it, is if there are more than two radial circuits and at least two of the circuits have the first device, a sounder located close to the CIE that would comply. Also if there is a dedicated sounder circuit and only one sounder is fitted close to the CIE, followed by as many radial circuits as you chose that would comply.
I am sure there are more configurations especially if you use ring circuits but, if this is correct then that is all I need to know.