The OV is obviously only of use when the fire service open it, until then you are relying on the S rated doorset to protect the stair. It will do so for a reasonable period of time. However (and as found by the BRE, BD2410 report) a 1sqm vent will not protect the stair when the flat door is open for anything length of time. Therefore, and appreciate fire fighters don't read these reports, small single stair buildings should be evacuated by the FRS before fire-fighting, or they should hope the wind is blowing in the right direction and the door at the base creates a stack flow effect increasing the extract potential of the roof vent, in which case it is possible to have a clear stair below the top storey.
If you cant get 1sqm OV then at least get one AOV top and bottom which will achieve same extract potential, as its B1 not B5.