Author Topic: AFD in purpose built block of flats -advice welcome!  (Read 32117 times)

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: AFD in purpose built block of flats -advice welcome!
« Reply #15 on: November 08, 2016, 11:17:55 AM »
Art 17 says "provided in respect of the premises under this Order or, subject to paragraph (6), under any other enactment."

Art 13 says "Where necessary," so if the if the sounders and call points are not necessary have they been provided in respect of the RR(FS)O or any other enactment and subject to art 17?

Ok, practical example. Large housing client with many 2 storey, small PB block of flats. All have emergency lighting installed, but they are not maintained or tested and there are no plans to do so due to cost. No requirement to install EL in the common stair when the blocks were built (1970s) or under the current ADB. At some point EL was installed but decision was taken not to test/maintain.

So, is said client in breach or Article 17 or not?

To me, yes they should, if the FRA considered it necessary, even if it wasn't a requirement under ADB in 1970s.


Same point then with the fire alarm, installed but not required, but should be maintained. Or remove it.  :)

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: AFD in purpose built block of flats -advice welcome!
« Reply #16 on: November 08, 2016, 01:06:24 PM »
I would think it is the RR(FS)O that rules the roost and if the FRA requires emergence lighting then it should be tested the statutory bar does not exist anymore. If not necessary I think it should be removed, the problem is, which legislation would you quote, bluff and persuasion act?
« Last Edit: November 08, 2016, 01:17:38 PM by Tom Sutton »
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: AFD in purpose built block of flats -advice welcome!
« Reply #17 on: November 08, 2016, 03:20:05 PM »
My point was that where a fire alarm has been installed in a purpose built block, when it wasn't deigned at built stage with said fire alarm, this was added later for reasons unknown. The extent of this fire alarm is AFD in the single common stair only and does not link into any flats, sounders, call point x 2 and panel are provided.

The system is not linked to any AOV's, as none required due to having no such requirement given the date of build, lets say late 1980's.

However, for whatever reason this fire alarm is not being tested (weekly as per the BS) or being maintained and the panel is showing fault.

Even though this fire alarm was not required at build stage and is still not required under ADB, is the RP in breach of Article 17 of the RRFSO for not maintaining and testing the fire alarm?
In my view they are in breach. Any opinions? where is Mr Todd when you need him? ???

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: AFD in purpose built block of flats -advice welcome!
« Reply #18 on: November 08, 2016, 03:29:21 PM »
PS I have housing clients that want to retain the common alarm (as it makes them feel safe  ::) but don't like sending the site manager once a week to test a call point in rotation!? I often get asked do you think we are in breach of the RRFSO or BS5839

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: AFD in purpose built block of flats -advice welcome!
« Reply #19 on: November 08, 2016, 07:47:52 PM »
I would think, that as the premises requires a FRA under the RR(FS)O and if a fire alarm is necessary, then the FA is subject to art 17. If it is not then there is no way of requiring him/her to take any action other than persuasion and make them fully aware, in writing of any possible problems that could arise.

It would be in breach of BS 5839 but the BS is only recommendation and good practice.
« Last Edit: November 08, 2016, 07:52:38 PM by Tom Sutton »
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: AFD in purpose built block of flats -advice welcome!
« Reply #20 on: November 09, 2016, 09:13:24 AM »
I would think, that as the premises requires a FRA under the RR(FS)O and if a fire alarm is necessary, then the FA is subject to art 17.

A fire alarm isn't necessary in this case though, in fact it is likely to cause more harm than good.

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: AFD in purpose built block of flats -advice welcome!
« Reply #21 on: November 09, 2016, 01:03:42 PM »
It's the same whatever aspect of fire protection you're talking about - if it's been installed and if it contributes to a reduction in fire risk then it should stay and has to be maintained.  This is basic risk assessment good practice and it applies whether the current codes/standards would recommend it or not.  The decision about whether you need to supply a risk reduction measure that isn't there at the moment is very different to the decision about taking out something that's there already (and therefore it must have been reasonably practicable to provide it).

If it doesn't contribute to a reduction in fire risk, then it can (and should) be decommissioned and removed.  If an RP leaves it in place, faulty and unmaintained then they're basically inviting enforcement action and whilst we can all speculate on how this would play in court, why invite that risk (and expense)?

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: AFD in purpose built block of flats -advice welcome!
« Reply #22 on: November 10, 2016, 07:35:52 PM »
My point was that where a fire alarm has been installed in a purpose built block, when it wasn't deigned at built stage with said fire alarm, this was added later for reasons unknown. The extent of this fire alarm is AFD in the single common stair only and does not link into any flats, sounders, call point x 2 and panel are provided.

The system is not linked to any AOV's, as none required due to having no such requirement given the date of build, lets say late 1980's.

However, for whatever reason this fire alarm is not being tested (weekly as per the BS) or being maintained and the panel is showing fault.

Even though this fire alarm was not required at build stage and is still not required under ADB, is the RP in breach of Article 17 of the RRFSO for not maintaining and testing the fire alarm?
In my view they are in breach. Any opinions? where is Mr Todd when you need him? ???

If you had a car and never took it on the road could you be prosecuted for not putting it through an MOT every year? (If that was the case). My point being that if it ain't necessary to have something you have do you have to keep it operational?
We're not Brazil we're Northern Ireland.

Offline Bruce89

  • Full Member
  • ***
  • Posts: 132
Re: AFD in purpose built block of flats -advice welcome!
« Reply #23 on: November 10, 2016, 08:38:07 PM »
Agree with fishy's posting, would add that as regards a fire authority taking a prosecution in regards to failing to maintain something that isn't necessary, I fail to see how that would be in the public interest which is one of the criteria applied in whether or not to prosecute. Most FA's are cash strapped these days and have more pressing priorities than an iffy prosecution which could leave them ?'s out of pocket.
That said never say never.

Offline nearlythere

  • Hero Member
  • *****
  • Posts: 4351
Re: AFD in purpose built block of flats -advice welcome!
« Reply #24 on: November 10, 2016, 09:03:45 PM »
Agree with fishy's posting, would add that as regards a fire authority taking a prosecution in regards to failing to maintain something that isn't necessary, I fail to see how that would be in the public interest which is one of the criteria applied in whether or not to prosecute. Most FA's are cash strapped these days and have more pressing priorities than an iffy prosecution which could leave them ?'s out of pocket.
That said never say never.
I can see a F&RS having any interest in pushing something like this. The bigger problem would likely be from a green horn fire safety officer on a promotion trip.
We're not Brazil we're Northern Ireland.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2477
    • http://www.firewizard.co.uk
Re: AFD in purpose built block of flats -advice welcome!
« Reply #25 on: November 10, 2016, 09:47:42 PM »
If I find something that can be removed or doesn't need maintaining as patently unnecessary and adding no value I make sure that the rationale is clearly explained in the FRA to demonstrate that it isn't part of any of the 'where necessary' requirements of the Order. It's also important that if there is something having to be left in situ but not operational it is clear to all relevant and responsible persons (especially in multi occupancies) so they aren't mislead - I've seen tenant FRAs that detail the wonderful protection provided by the sprinkler system in their building despite it having been drained down years ago......
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Bruce89

  • Full Member
  • ***
  • Posts: 132
Re: AFD in purpose built block of flats -advice welcome!
« Reply #26 on: November 11, 2016, 08:06:39 AM »
Hopefully the green horn fire safety officer on a promotion trip would have sufficient line management to report to who should be calming him/her down and pointing out the error of their ways, besides I suspect most brigades have a policy that requires high level authorisation before going to prosecution.

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: AFD in purpose built block of flats -advice welcome!
« Reply #27 on: November 11, 2016, 11:45:17 AM »
Hopefully the green horn fire safety officer on a promotion trip would have sufficient line management to report to who should be calming him/her down and pointing out the error of their ways, besides I suspect most brigades have a policy that requires high level authorisation before going to prosecution.



 ;D That made me smile

Offline Bruce89

  • Full Member
  • ***
  • Posts: 132
Re: AFD in purpose built block of flats -advice welcome!
« Reply #28 on: November 11, 2016, 06:42:52 PM »
??

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: AFD in purpose built block of flats -advice welcome!
« Reply #29 on: November 12, 2016, 09:19:10 AM »
??

The chances of you finding a situation as per your statement are slim in my experience.