BS 9999: 2017
« on: January 09, 2017, 09:09:29 AM »
Revised standard has now been published ...
http://shop.bsigroup.com/ProductDetail?pid=000000000030314118

Offline Bruce89

  • Full Member
  • ***
  • Posts: 132
Re: BS 9999: 2017
« Reply #1 on: January 09, 2017, 07:10:11 PM »
Thanks for the heads up.

Offline lyledunn

  • Hero Member
  • *****
  • Posts: 503
Re: BS 9999: 2017
« Reply #2 on: February 24, 2017, 07:19:32 AM »
I note that issue of the standard has been stopped. Reason given was information included was dangerous!

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: BS 9999: 2017
« Reply #3 on: February 24, 2017, 03:09:11 PM »
I note that issue of the standard has been stopped. Reason given was information included was dangerous!

One of the lesser-used tables recommended 30 mins fire resistance instead of 60 mins fire resistance for a particular building configuration and use.  Whilst this might certainly have safety implications... "dangerous" ???

Offline Revol

  • Jr. Member
  • **
  • Posts: 71
Re: BS 9999: 2017
« Reply #4 on: March 10, 2017, 09:54:57 AM »
Do we know where the error is? ... I'm taking a wild stab in the dark but, 2008 Rev recommenced 60 mins FR to an Assembly building: ordinary hazard (no sprinklers), less than 5 meters (Table 25), in the 2017 Rev 30 mins FR is recommended for a B2 risk profile less than 5 meters (Table 23)

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: BS 9999: 2017
« Reply #5 on: March 10, 2017, 10:13:51 AM »
It wasn't in Table 23 - it was Table 24 Fire resistance periods for elements of structure (based on the ventilation conditions given in Table 25), - the sixth column was a 30 when it should have been a 60 but you'll only see it if you downloaded the original version - the one you'll get if you download it now has been corrected, I believe.

Offline Revol

  • Jr. Member
  • **
  • Posts: 71
Re: BS 9999: 2017
« Reply #6 on: March 10, 2017, 12:54:02 PM »
It wasn't in Table 23 - it was Table 24 Fire resistance periods for elements of structure (based on the ventilation conditions given in Table 25), - the sixth column was a 30 when it should have been a 60 but you'll only see it if you downloaded the original version - the one you'll get if you download it now has been corrected, I believe.

Thanks Fishy ... I better get my tippex out!