I have been asked advice on a warehouse that is approx 1000 x 50 sqm that currently has no fire alarm system installed.

The warehouse is all open plan, one area with no other compartments with a max of 5 staff working in there with numerous exits.

If a fire was to start in there it would be visible and obvious to the staff working there, therefore I am inclined to say automatic FD is not required with an alternate method provided.

What are others thoughts on this as I am aware the interpretation is open to debate where some say alarm systems are needed almost everywhere and others on the specific circumstances.

Thanks

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Fire Alarm System in Warehouse
« Reply #1 on: February 16, 2017, 12:28:37 PM »
Just confirm the building dimensions please James

Offline James Farmer

  • Newbie
  • *
  • Posts: 11
Re: Fire Alarm System in Warehouse
« Reply #2 on: February 16, 2017, 12:34:09 PM »
Sorry my mistake just checked their response 100 x 50

Thanks

Offline Bruce89

  • Full Member
  • ***
  • Posts: 132
Re: Fire Alarm System in Warehouse
« Reply #3 on: February 16, 2017, 04:08:22 PM »
Appears from what you are describing a type M would suffice.

Offline jayjay

  • New Member
  • Sr. Member
  • *
  • Posts: 278
Re: Fire Alarm System in Warehouse
« Reply #4 on: February 16, 2017, 10:21:20 PM »
If as you say all areas can be seen by the employees then what extra is a fire warning system going to provide?

Detection would be no quicker than observation and if a person discovering and then shouting fire could be heard by all occupants above any background noise what is the point of installing a fire warning system. Shouting fire could be quicker warning than moving to a call and operating it.

Provided this is written in as the fire procedure then it should be compliant with the regulations.

Offline James Farmer

  • Newbie
  • *
  • Posts: 11
Re: Fire Alarm System in Warehouse
« Reply #5 on: February 17, 2017, 09:42:18 AM »
Thanks for the replies.

I agree jayjay I would be very reluctant to tell a business they need to spend on an alarm system when the benefits are no greater unless their insurer required it.

You come across some that say yes you must have some type of electronic fire alarm system regardless which is not true but then you find they sell nd install them.

Offline Bruce89

  • Full Member
  • ***
  • Posts: 132
Re: Fire Alarm System in Warehouse
« Reply #6 on: February 17, 2017, 05:24:09 PM »
Unless normal sound levels within the building are very low I doubt shouting fire would be sufficient in a building the size you describe combined with storage probably at various heights and configuration which would affect how the sound travels, only way to be sure would be an audibility test at different locations in the building during normal operating conditions.

Offline Davo

  • Hero Member
  • *****
  • Posts: 1144
Re: Fire Alarm System in Warehouse
« Reply #7 on: February 17, 2017, 07:16:46 PM »
James

as bruce says, voice would be OK in an empty warehouse.
However, you are storing items, to what height, density and size?
Sources of ignition?
What about toilet linkage, staff disability eg strobe sounders etc?

davo

Offline James Farmer

  • Newbie
  • *
  • Posts: 11
Re: Fire Alarm System in Warehouse
« Reply #8 on: February 17, 2017, 08:33:21 PM »
Hi

Thanks for the replies.

I understand the arguments for both, the place in question is local to me so I have told them I will pop by.

At the same time bring up the FRA but I doubt they have one considering they are asking the questions unless they are attempting to question it.

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire Alarm System in Warehouse
« Reply #9 on: February 20, 2017, 10:59:55 PM »
Bruce Almighty, they are not called type M , they are called category M.  And the voice of an irate London I/) can be heard from the city of London all the way down to Guildford, never mind a wee warehouse.
Colin Todd, C S Todd & Associates

Offline Bruce89

  • Full Member
  • ***
  • Posts: 132
Re: Fire Alarm System in Warehouse
« Reply #10 on: February 23, 2017, 11:47:08 AM »
You are of course correct colski but the fact you knew what I was referring to says it all  ;)

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: Fire Alarm System in Warehouse
« Reply #11 on: February 23, 2017, 01:25:57 PM »
Bear in mind that shouting is not the only way or raising the alarm without an alarm system, rotary gongs, air horns, tannoy systems etc. still fall into the category M systems.
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2480
    • http://www.firewizard.co.uk
Re: Fire Alarm System in Warehouse
« Reply #12 on: February 23, 2017, 06:06:20 PM »
Manual means of raising the alarm - yes, suitable in certain circumstances - yes, Category M systems, no, the terminology is part of BS5839-1 and none of those would meet the requirements of that standard.

Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline colin todd

  • Hero Member
  • *****
  • Posts: 3473
  • Civilianize enforcement -you know it makes sense.
    • http://www.cstodd.co.uk
Re: Fire Alarm System in Warehouse
« Reply #13 on: February 25, 2017, 06:58:08 PM »
Tony is right Buckers.