Nothing wrong with keeping CO2. Many subs still have them, although often they are the mechanical pull station/fusible link ones (which still work more than adequately if maintained), if you are lucky it may be a rudimentary electromechanical one.
I've seen the following done with existing subs:
1) Rip all existing stuff out & have nothing but AFD & PEA
2) Leave existing system in unaltered (with out of test cylinders)
3) Keep existing system, ensure all cylinders are within test date having them retested as required
4) Emulsifying water sprinklers installed (more recently water mist is being used instead)
5) Clean agent gas system, eg. Argonite, Inergen, FM200
Rarely you'll find a sub with BCF, only found that twice, in one case it was an old Methyl Bromide system where GFA refurbed the cylinders to to BCF in the late 60s
With existing basement subs refurbing the existing CO2, having nothing, or clean agent are the most common i've seen.
New subs mostly have nothing other than AFD/PEA, the few that have anything are Water Mist or Clean agent