Author Topic: emergency lighting testing  (Read 3130 times)

Offline PGtips

  • Jr. Member
  • **
  • Posts: 71
emergency lighting testing
« on: July 23, 2019, 08:57:10 AM »
Hi all - just browsing BS9999:2017 as you do and find the under six monthly maintenance recommendations, testing emergency and escape lighting systems pops up as requiring an inspection and testing by a competent person.

My understanding was that the requirement was monthly and annual - what am I missing? Most companies offer their services on a monthly and annual basis as well.....

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2477
    • http://www.firewizard.co.uk
Re: emergency lighting testing
« Reply #1 on: July 23, 2019, 07:48:37 PM »
You aren't missing anything, it's yet another mistake in BS9999. BS5266 removed the 6 monthly part duration test in 2004.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Fishy

  • Hero Member
  • *****
  • Posts: 777
Re: emergency lighting testing
« Reply #2 on: July 25, 2019, 12:14:03 PM »
...although there are some instances where BS 9999 deliberately contradicts the 'system' standards - e.g. power supplies to evacuation lifts, where BS 9999 recommendations are less onerous than BS 8519.  Not suggesting the same applies with this particular issue - although it might...

Offline PGtips

  • Jr. Member
  • **
  • Posts: 71
Re: emergency lighting testing
« Reply #3 on: August 09, 2019, 02:22:30 PM »
Arghhh!  Thanks again for the info guys - just got that Friday feeling!