Post by: wavecrest on February 04, 2009, 05:21:31 PM
Good afternoon. My name is Glen and I have a question which I guess would be best directed at Fire Investigations Officers who are members of this site...

My company operates a warehouse facility in Kent. Last year we had a very serious fire at one of our warehouse units which took several days to put out (the warehouse was mainly storing paper goods). Fortunately the fire was at night so there were no injuries to staff. Unfortunately the building was completely destroyed.

It would appear that the cause of the fire was failure of a battery charger which was being used to charge an electric fork lift truck overnight.

My question is whether any members are aware of similar cases they have investigated/attended where a fork lift battery charger has caused a fire?

I am trying to find out how common this type of fire is in the UK and evidence of similar incidents to ours.

Any information would be useful as the company which supplied the battery charger are trying to deny responsibility although all the evidence turned up so far clearly points in their direction!

Thanks in advance.
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: kurnal on February 04, 2009, 09:51:13 PM
People always deny responsibility. You will have to prove their negligence to win this, to estabish that they had a duty of care, that they were in breach of this duty and how, and that the fire occurred as a result.

Where did the fault arise? In the charger, the battery, the wiring to the charger or the protective systems? Was the system properly maintained? I see so many of these things in a poor condition through misuse and neglect- chafed and crushed leads, missing grommets, poor connections. Its a wonder theres not more fires. Some of these things charge at huge currents but very often are intelligent and monitored.
Was a fire investigation carried out at the time?  Have you a copy of the report? Why do you think the manufacturers are responsible- can you show the electrical systems and protective devices were in good order?
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: afterburner on February 05, 2009, 08:42:31 AM
Hi Glen, the post from Kurnal addresses all the issues on this incident. The frequency of an event is not an indicator of a universal cause. No matter how many fires are attributed to fork lift truck battery chargers, the same considerations apply.   
The source of ignition may be traceable all the way back to the battery charger. But was the battery charger actually at fault? Can you be sure that the charger was tested and maintained within the manufacturers specifications? Was it used as it should be, or were there 'habit and practice' departures from correct use?
Do you know what component actually failed within the charger? Was this due to a design fault, poor manufacture, lack of maintenance etc?
Without being able to answer these questions to show that the fire was caused by propely maintained and correctly used charger you might have a real struggle to prove liability 
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: Chris Houston on April 10, 2010, 11:31:54 PM
I'd say that battery charging is a common cause of fire in industrial premises.  I can think of 1 fairly recent example at a client's premises in the UK.
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: afterburner on April 13, 2010, 01:59:48 PM
Quite agree Chris that the process of battery charging is a hazard recognisable as a start point for fires.

But what we were trying to clarify is what went wrong within the process. If the battery charging process is successfully carried out a number of times without a fire as a result, what is the actual 'event' that changes battery charging into ignition? The deeper cause could be a number of things, from various faults to operator error.
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: Chris Houston on April 13, 2010, 03:35:09 PM
Quite agree Chris that the process of battery charging is a hazard recognisable as a start point for fires.

But what we were trying to clarify is what went wrong within the process. If the battery charging process is successfully carried out a number of times without a fire as a result, what is the actual 'event' that changes battery charging into ignition? The deeper cause could be a number of things, from various faults to operator error.

Of course, lots of things could have gone wrong.  Battery charging creates hydrogen gas.  Combination of a spark igniting gas and combustibles being in the wrong place at the wrong time would be the most common scenario.

Risk controls of ventilation to prevent gas building up, electrical maintenance to avoid sparks and removal of combustible items from withing x metres from charging point would all be good idea, obviously a bit late to make suggestions.
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: BLEVE on May 30, 2010, 10:13:13 PM
In reality battery charging activities should be segregated from all other combustible materials. My preference is either to sepaate with consruction offering Fr 60 minutes or separate by distance to reduce Radiant Heat below 20 KW/M^2

Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: nearlythere on May 30, 2010, 11:16:05 PM
or separate by distance to reduce Radiant Heat
Hello Bleve
How does one determine the distance  necessary to reduce the radiant heat to below 20 KW/M^2?
What equipment does the average electric forklift truck owner need to buy to do the necessary measuring to ensure that the distance is sufficient?
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: Meerkat on June 01, 2010, 09:45:25 AM
In the reality I have experienced, battery charging areas tend to get pushed into a corner of the factory or warehouse.  They certainly don't have fire resisting separation in most of the premises I have seen and the distance separation has more to do with making sure there's enough room to safely manouevre the trucks in and park them without anyone else hitting them while driving by than it does with radiant heat output!

Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: BLEVE on June 02, 2010, 02:34:20 PM
Nearly there,

You take into account the following:

Peak Heat Release Rate of the lift truck & charger
% of combustion energy lost by flame as radiation
distance from flame axis to target fuel source


Assuming an overly conservative PHRR of 2000 kW
Xrof 0.6 (high soot content from rubber wheels & plastics)

Distance to 20 kW/m2 is 2.2. metres

As you know the 20 kW/m2 relates to the piloted ignition of thermally thick materials so it would be better to opt for 10 kW/m2 piloted ignition of thermally thin materials and so distance to 10 10 kW/m2 is 3.2 metres.

Tools required are PC or calculator and tape measure/yard stick etc.

 :)

Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: nearlythere on June 02, 2010, 02:49:50 PM
Nearly there,

You take into account the following:

Peak Heat Release Rate of the lift truck & charger
% of combustion energy lost by flame as radiation
distance from flame axis to target fuel source


Assuming an overly conservative PHRR of 2000 kW
Xrof 0.6 (high soot content from rubber wheels & plastics)

Distance to 20 kW/m2 is 2.2. metres

As you know the 20 kW/m2 relates to the piloted ignition of thermally thick materials so it would be better to opt for 10 kW/m2 piloted ignition of thermally thin materials and so distance to 10 10 kW/m2 is 3.2 metres.

Tools required are PC or calculator and tape measure/yard stick etc.

 :)


Thanks Bleve. Well explained.
Anyone got a headache tablet?
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: Midland Retty on June 02, 2010, 03:04:25 PM
I feel somewhat inadequate and a bit afraid

Even my calculator has blown up !

Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: kurnal on June 02, 2010, 06:01:28 PM
Interesting approach to a common  situation Bleve but is it realistic to expect charging to take place in a segregated area? In my experience in at least 90% of warehouses the charging area is not segregated from the rest of the building.  And in some cases charging is continuous from busbars in the aisles as the truck goes about its business.

I wonder if you apply a quantitative approach to all aspects of your risk assessments or do you tend to use a hybrid approach?  I tend to rely on a qualitative apporach for the majority of my work.
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: BLEVE on June 02, 2010, 06:41:21 PM
Hi Kurnal,
Typically segregation by FR construction is only carried out when requested by insurance underwriters or considered by me in relation to very high value pharma/bio tech product.

I will frequently use a quantatitive approach to either prove or disprove a thesis depending on the task in hand. I tend to prefer quantatitive approach in the majority of my RA, particularly so in the case of fire risk assessment, thermal heat flux, smioke evolution, time to obscuartion and means of escape. 

I like to use a rule of thumb of separating charging activities from combustibles by a distance of at least 5 metres.

Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: BLEVE on June 02, 2010, 07:26:54 PM
Meerkat,
It is apparent and widely accepted that lift truck charging operations can and do result in fires. Taking this into account, it is only reasonable that a RA takes into account the likely HRR resulting from the fire and to determine an appropriate separation by distance to prevent the involvement and ignition of secondary fuel sources.

Just because it is normal for these activities to be placed in any available location does not mean that it is correct to do so.

 
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: kurnal on June 02, 2010, 08:31:27 PM
I agree with most of what you say Bleve but whilst most of my customers would happily accept the need for greater care to prevent fires and mitigation of their effects- maintenance, housekeeping, tests and inspections, sensible spacing of the charging area from combustibles, ventilation if necessary, fire fighting equipment, i feel most would accuse me of being OTT if I started to ask for existing, well managed charging areas to be enclosed in their own fire compartment within an existing building.

On a similar theme I am about to start a new topic on standards in B&Bs  and guest houses having stayed in three over the last weekend, none of which had given any consideration whatsoever to fire safety. It made me question what was reasonable. In one of them I would not have been able to produce an action plan that would have even approached national guidance- but they used to have a fire certificate! Made me question my own standards and wonder if I am sometimes unrealistic in my expectations.
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: nearlythere on June 02, 2010, 10:07:27 PM
I agree with most of what you say Bleve but whilst most of my customers would happily accept the need for greater care to prevent fires and mitigation of their effects- maintenance, housekeeping, tests and inspections, sensible spacing of the charging area from combustibles, ventilation if necessary, fire fighting equipment, i feel most would accuse me of being OTT if I started to ask for existing, well managed charging areas to be enclosed in their own fire compartment within an existing building.

On a similar theme I am about to start a new topic on standards in B&Bs  and guest houses having stayed in three over the last weekend, none of which had given any consideration whatsoever to fire safety. It made me question what was reasonable. In one of them I would not have been able to produce an action plan that would have even approached national guidance- but they used to have a fire certificate! Made me question my own standards and wonder if I am sometimes unrealistic in my expectations.
Therein lies the rub K. All fire safety measures are over the top, until there is a fire.
But the chances are they won't have one.
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: BLEVE on June 03, 2010, 08:18:37 AM
At the end of the day we can only provide advice, whether it is acted upon is down to the client.

Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: Davo on June 06, 2010, 08:53:05 AM
IMHO

Going by the book on battery charging areas would close hundreds of businesses. Lets be sensible.

Would you insist we all change to car X as it is the safest in a crash?
Would you ban Chelsea Tractors as they cause most damage to the other vehicle?


davo
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: BLEVE on June 06, 2010, 09:54:00 AM
I dont see how keeping combustible materials a distance of 2.2-3.2 metres away from a lift truck charging point would close down hundreds of businesses.

At the end of the day, charging point fires ocurr and unless extinguished, result in fire fire spread. Separation by distance may well prevent further fire spread, loss of property and or life.

Car design or model selection has nowt to do with it.

In the main, within the UK fire safety legislation concentrates on life safety. Within other countries the legislation and standards look towards simultaneous property protection and life safety.  We should remember that there are more frequent and also serious consequences in terms of property damage, loss of livelihoods, environmental damage associated with the outbreak of a fire.

Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: Davo on June 06, 2010, 11:30:07 AM
BLEVE

Very much agree with last para!

What I am saying is don't rely on statistics, unrealistic testing eg fire doors without seeking real life experiences.
Those guys who have got the tee shirt (doffs cap) will tell you a fire door could go in as little as 8 minutes depending on circumstances


davo
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: BLEVE on June 06, 2010, 12:59:39 PM
Davo,
That is exactly what I am saying. For intsnace I have seen fire risk assessment reports applicable to sleeping risk premises overlooking or automatically accepting that a nominal georgian wired glass top and bottom panel door is rated as a FD30 door. When had they been capable of assessing the door, they would have noticed that the door had no insulative properties and the glazing retaining system was unsuitable. Given the situation in question the door would be lucky to last 10 minutes. On a connected matter the door was devoid of cold smoke seal and given the leakage rates anticipated, this would have put a great number of non ambulant people in harms way.

As I have said before, I will typically evaluate the risk with a combination of calculation and experience of fire/smoke.

 
Title: Re: FIRE CAUSED BY BATTERY CHARGER
Post by: kurnal on June 06, 2010, 01:57:13 PM
For intsnace I have seen fire risk assessment reports applicable to sleeping risk premises overlooking or automatically accepting that a nominal georgian wired glass top and bottom panel door is rated as a FD30 door. When had they been capable of assessing the door, they would have noticed that the door had no insulative properties and the glazing retaining system was unsuitable. Given the situation in question the door would be lucky to last 10 minutes.

Your point is very valid  but each situation is different and needs to be judged on its own merit. There are millions of doors constructed to older standards up and down the country and the knife edge we have to walk is providing a balanced view. Many doors installed in the 1960s for example had superb standards of joinery but were very poor in terms of glazing. Many of us have seen georgian wired glazing slump out of the frame as a result of exposure to fire.

We must of course  recognise that some doors are more important for their smoke control properties than their integrity - if the buildings are  managed correcly many of the doors on protected routes are unlikely to ever be exposed to the full radiated heat flux of a fire?

These decisions are never easy- its simple to measure an individual building against the design guidance and produce an action plan. But if your client has say 1500 such properties and all are in similar condition and design (eg social housing provision transferred out of former local concil stock) then a more pragmatic view needs to be taken.

No good setting targets and objectives that cannot be achieved. Prioritisation is the key.