		THE REGULATORY REFORM (FIRE SAFETY) ORDER 2005 => Guides and Legislation Links => Topic started by: Revol on January 09, 2017, 09:09:29 AM
		
			
			- 
				Revised standard has now been published ...
 http://shop.bsigroup.com/ProductDetail?pid=000000000030314118
 
- 
				Thanks for the heads up.
			
- 
				I note that issue of the standard has been stopped. Reason given was information included was dangerous!
			
- 
				I note that issue of the standard has been stopped. Reason given was information included was dangerous!
 
 
 One of the lesser-used tables recommended 30 mins fire resistance instead of 60 mins fire resistance for a particular building configuration and use.  Whilst this might certainly have safety implications... "dangerous" ???
- 
				Do we know where the error is? ... I'm taking a wild stab in the dark but, 2008 Rev recommenced 60 mins FR to an Assembly building: ordinary hazard (no sprinklers), less than 5 meters (Table 25), in the 2017 Rev 30 mins FR is recommended for a B2 risk profile less than 5 meters (Table 23)
			
- 
				It wasn't in Table 23 - it was Table 24 Fire resistance periods for elements of structure (based on the ventilation conditions given in Table 25),  - the sixth column was a 30 when it should have been a 60 but you'll only see it if you downloaded the original version - the one you'll get if you download it now has been corrected, I believe.
			
- 
				It wasn't in Table 23 - it was Table 24 Fire resistance periods for elements of structure (based on the ventilation conditions given in Table 25),  - the sixth column was a 30 when it should have been a 60 but you'll only see it if you downloaded the original version - the one you'll get if you download it now has been corrected, I believe.
 
 
 Thanks Fishy ... I better get my tippex out!