What if you have an open riser going through several floors. A detector would be mounted at the top. Would it be required to have a detector also outside the riser as you would a lift? Or am I missing the point?
As I previously advised, yes it would. Any flue-like structure penetrating through floors requires it - smoke sealed doors or not! (just in case the door was left open or the seals didn't work?). BS 5839 part 1 2002 22.2.C) refers.
Please note that the detector needs to be on the 'accommodation' side and not in the flue-like structure (apart from the one at the top of the flue-like structure, of course) and you only need it IF the accommodation side of the flue-like structure is an area that would require detection anyway by virtue of the system category designation.