Author Topic: Fire detection in lift lobby ?  (Read 14728 times)

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Fire detection in lift lobby ?
« Reply #15 on: November 27, 2008, 08:52:11 PM »
We must remember that most service risers are protected shafts with fire resisting doors provided with smoke seals.

Lift shafts are a little different as these are the only fire doors in Approved Document B not required to have smoke seals- this is always imossible to achieve in a sliding door.

Offline Benzerari

  • Hero Member
  • *****
  • Posts: 1391
    • http://benzerari.tripod.com/fas/
Re: Fire detection in lift lobby ?
« Reply #16 on: November 27, 2008, 09:24:27 PM »
Also most risers I have seen have detectors inside in each floor, while in lift shaft has only one in the top...

Offline Big_Fella

  • Full Member
  • ***
  • Posts: 232
Re: Fire detection in lift lobby ?
« Reply #17 on: November 28, 2008, 08:27:33 AM »
What if you have an open riser going through several floors.  A detector would be mounted at the top.  Would it be required to have a detector also outside the riser as you would a lift?  Or am I missing the point?
** Knowledge is power, I'm still working on both **

Offline Wiz

  • Hero Member
  • *****
  • Posts: 1591
Re: Fire detection in lift lobby ?
« Reply #18 on: November 28, 2008, 10:04:28 AM »
What if you have an open riser going through several floors.  A detector would be mounted at the top.  Would it be required to have a detector also outside the riser as you would a lift?  Or am I missing the point?

As I previously advised, yes it would. Any flue-like structure penetrating through floors requires it - smoke sealed doors or not! (just in case the door was left open or the seals didn't work?). BS 5839 part 1 2002 22.2.C) refers.

Please note that the detector needs to be on the 'accommodation' side and not in the flue-like structure (apart from the one at the top of the flue-like structure, of course) and you only need it IF the accommodation side of the flue-like structure is an area that would require detection anyway by virtue of the system category designation.
« Last Edit: November 28, 2008, 11:48:23 AM by Wiz »