No they dont GFSM but it is interesting for comparison purposes. It does work out at about 2.5mm/sqm/minute if you calculate the nozzle discharge divided by the area of coverage of the head. It becomes relevant when you need to argue with developers who wish to install domestic sprinkers in commercial situations. And especially in view of the limited duration of the supply.
For example, in the same way ESFR sprinklers often do not refer to design densities but I recently asked for this information from the designer/installer when we were pushing the envelope in a warehouse. This was to cover a new risk in an existing warehouse in which ESFR was already installed. No risk specific design data was available for an ESFR system but data was available for conventional systems. The D/D from the ESFR was shown to be in excess of 90mm/min, BSEN12845 would have recommended HSS with 12.5mm in this storage configuration so the insurers were satisfied.