Author Topic: Design Density for Domestic Sprinklers  (Read 12537 times)

Offline GB

  • Full Member
  • ***
  • Posts: 234
Design Density for Domestic Sprinklers
« on: December 17, 2010, 12:36:44 PM »
Does anyone know of a recognised design density of water for a domestic sprinkler system ::)

Offline FSO

  • Full Member
  • ***
  • Posts: 216
Re: Design Density for Domestic Sprinklers
« Reply #1 on: December 17, 2010, 07:21:45 PM »
From a quick calculation in my head, I think it is about 2.8. I stand to be corrected though.

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Re: Design Density for Domestic Sprinklers
« Reply #2 on: December 18, 2010, 08:14:57 AM »
Chaps,

Calcs for domestic sprinklers do not use design densities.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Design Density for Domestic Sprinklers
« Reply #3 on: December 18, 2010, 08:49:00 AM »
No they dont GFSM  but it is interesting for comparison purposes. It does work out at about 2.5mm/sqm/minute if you calculate the nozzle discharge divided by the area of coverage of the head. It becomes  relevant when you need to argue with developers who wish to install domestic sprinkers in commercial situations. And especially in view of the limited duration of the supply.

For example, in the same way ESFR sprinklers often do not refer to design densities but I recently asked for this information from the designer/installer when we were pushing the envelope in a warehouse. This was to cover a new risk in an existing warehouse in which ESFR was already installed. No risk  specific design data was available for an ESFR system but data was available for conventional systems. The D/D from the ESFR  was shown to be in excess of 90mm/min, BSEN12845 would have recommended HSS  with  12.5mm in this storage configuration so the insurers were satisfied.
« Last Edit: December 18, 2010, 08:53:27 AM by kurnal »

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Re: Design Density for Domestic Sprinklers
« Reply #4 on: December 18, 2010, 09:33:39 AM »
I thought if there were ever such a DD for domestic sprinklers it was more like 4mm seeing as domestic flow requirements are 60 l/min for 1 head / 15 sqm.

But I'm sure I would benefit from a breakdown of how 2.8mm is achieved - after all one never stops learning in the dark arts.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Design Density for Domestic Sprinklers
« Reply #5 on: December 18, 2010, 12:07:27 PM »
Yes thats the design criteria for the water supply but what actually comes out of the head is the product of the K factor and the square root of the pressure. A typical K factor would be 60.
The minimum pressure requirement at the most unfavourable head is a minimum of 0.5 Bar for a BS7259 system so the actual output may be as low as 15 litres per minute. In actual fact it is unlikely to be as low as this as most systems would be designed to better the minimum criteria.
« Last Edit: December 18, 2010, 12:09:33 PM by kurnal »

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Re: Design Density for Domestic Sprinklers
« Reply #6 on: December 18, 2010, 01:03:03 PM »
Well I would work that out to be a pressure at the MUH of 1 bar assuming domestic req for 60 l/min. Twice the minimum requirement, but a BS 7259 system I've not heard of.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Re: Design Density for Domestic Sprinklers
« Reply #7 on: December 18, 2010, 01:57:53 PM »
Neither have I. Of course it should have been BS 7251 ;)

Must point out that I am pretty well self taught when it comes to sprinklers and the instructor was rubbish.
« Last Edit: December 18, 2010, 03:37:57 PM by kurnal »

Offline deaconj999

  • Jr. Member
  • **
  • Posts: 96
Re: Design Density for Domestic Sprinklers
« Reply #8 on: December 18, 2010, 04:06:18 PM »
Kurnal,

You are wiser than me without doubt, in cases of 7251 read 9251  ::)

Offline Phoenix

  • Hero Member
  • *****
  • Posts: 677
  • Get a bicycle. You will not live to regret it
    • MetaSolutions (Fire Safety Engineering) Ltd.
Re: Design Density for Domestic Sprinklers
« Reply #9 on: December 18, 2010, 06:33:51 PM »
This is where the 2.8mm/minute comes from:

Water flow requirement for domestic is 60 litres/min from one head or 42 litres/min from each of two heads in the same room.  So the system must be capable of delivering a flow of at least 84 litres/min at the most hydraulically unfavourable location (i.e. furthest from and highest above the main valve).  The coverage is 15m2 max. 

Bear in mind that a lot of systems will deliver more than the minimum but let's suppose that a system is delivering the minimum of 84 litres/minute over the maximum area of 15m2 x 2 (as two heads are operating) = 30m2.  84 litres equals a volume of 0.084m3

0.084/30 = 0.0028m = 2.8mm

It's 84 litres per minute so the equivalent design density is 2.8mm/min.

If only one head operates then we expect 60 litres per minute to be delivered which will be at a density of 4mm/minute (0.06/15).  The system should be capable of satisfying both requirements.

Residential systems are slightly different.


Stu


Offline H2OFS

  • Newbie
  • *
  • Posts: 3
    • Fire Sprinklers
Re: Design Density for Domestic Sprinklers
« Reply #10 on: December 27, 2010, 12:14:46 AM »
This is where the 2.8mm/minute comes from:

Water flow requirement for domestic is 60 litres/min from one head or 42 litres/min from each of two heads in the same room.  So the system must be capable of delivering a flow of at least 84 litres/min at the most hydraulically unfavourable location (i.e. furthest from and highest above the main valve).  The coverage is 15m2 max. 

Bear in mind that a lot of systems will deliver more than the minimum but let's suppose that a system is delivering the minimum of 84 litres/minute over the maximum area of 15m2 x 2 (as two heads are operating) = 30m2.  84 litres equals a volume of 0.084m3

0.084/30 = 0.0028m = 2.8mm

It's 84 litres per minute so the equivalent design density is 2.8mm/min.

If only one head operates then we expect 60 litres per minute to be delivered which will be at a density of 4mm/minute (0.06/15).  The system should be capable of satisfying both requirements.

Residential systems are slightly different.


Stu



Good answer, residential requirement is 4 heads in the same room at 42 litres/min running for 30mins.