Author Topic: CO2 Gas Suppression System.  (Read 9137 times)

Offline hammer1

  • New Member
  • Full Member
  • *
  • Posts: 157
CO2 Gas Suppression System.
« on: September 24, 2009, 10:43:01 AM »
When is a integrity test require as part of the maintenance regime. Obviously on installation, but is there any recommendations to carry out test thereafter???

Offline jimbosdad

  • Newbie
  • *
  • Posts: 7
Re: CO2 Gas Suppression System.
« Reply #1 on: September 24, 2009, 01:05:04 PM »
You need to check BSEN 15004  ;)

Offline hammer1

  • New Member
  • Full Member
  • *
  • Posts: 157
Re: CO2 Gas Suppression System.
« Reply #2 on: September 24, 2009, 03:36:54 PM »
I have been informed Integrity Testing is a mandatory requirement of BS ISO 14520 and should be undertaken annually or as often as is recommended by the competent contractor???

Any takers on that advice

Online AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2492
    • http://www.firewizard.co.uk
Re: CO2 Gas Suppression System.
« Reply #3 on: September 24, 2009, 04:11:54 PM »
Both BS 5306-4:2001 & ISO 14520-1:2000 say that at the 12 month service an integrity test is required, at the intervening 6 month service only the pipework, valves & cylinders need checking.

Truthfully in my experience integrity re-testing of inert/halon/halocarbon systems is rare enough, but for CO2 systems (most of which I find are 25-40 years old) is almost never done (nor is other testing!)
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

Offline Tom Sutton

  • Hero Member
  • *****
  • Posts: 2287
Re: CO2 Gas Suppression System.
« Reply #4 on: September 24, 2009, 08:40:46 PM »
It appears ISO 14520-1:2000 has been withdrawn. BS EN 15004-1:2008 Fixed firefighting systems - Gas extinguishing systems - Design, installation and maintenance together with BS 5306-4:2001 - Fire extinguishing installations and equipment on premises - Specification for carbon dioxide systems seems to be the current ones.
All my responses only apply to England and Wales and they are an overview of the subject, hopefully it will point you in the right direction and always treat with caution.

Offline hammer1

  • New Member
  • Full Member
  • *
  • Posts: 157
Re: CO2 Gas Suppression System.
« Reply #5 on: September 24, 2009, 08:52:09 PM »
Both BS 5306-4:2001 & ISO 14520-1:2000 say that at the 12 month service an integrity test is required, at the intervening 6 month service only the pipework, valves & cylinders need checking.

Truthfully in my experience integrity re-testing of inert/halon/halocarbon systems is rare enough, but for CO2 systems (most of which I find are 25-40 years old) is almost never done (nor is other testing!)

Makes you wonder, when in those last 25-40 years the amount of new cabling that may have been replaced/re-feed  and a possibility that works has been carried out in and around the area concerned which could of compromised the compartmentation. The area covered has to be well-sealed so that your gaseous agent won't escape causing the fire to possibly re-ignite.

Anyway, that's enough wondering for one day ;D

Offline Allen Higginson

  • Hero Member
  • *****
  • Posts: 1131
Re: CO2 Gas Suppression System.
« Reply #6 on: September 24, 2009, 11:13:10 PM »
I've never known a room integrity test to be done for CO2 - I had assumed that this was down to the difference in how it extinguishes compared to chemical agents.

Offline CivvyFSO

  • Hero Member
  • *****
  • Posts: 1583
Re: CO2 Gas Suppression System.
« Reply #7 on: September 25, 2009, 01:45:04 AM »
From BS5306-4:2001

9.2.2 User’s programme of inspection
The user shall obtain from the installer an inspection programme for the system and its components. The
programme shall include instructions on the action to be taken in respect of faults.
NOTE The user’s inspection programme is intended to detect faults at an early stage to allow rectification before the system may
have to operate. A suitable programme is as follows.
a) Weekly Visually check the hazard and the integrity of the enclosure for changes which might reduce the efficiency of the system.


Ha! I can see that one getting done everywhere too!

Offline Psuedonym

  • Sr. Member
  • ****
  • Posts: 315
Re: CO2 Gas Suppression System.
« Reply #8 on: October 10, 2009, 08:49:59 PM »
Room integrety testing should be carried out prior to installaton of any gas extinguishing system and at intervals as per BSEN 15004:1 2008. However following any works which may have breached a compartments integrity, testing should be carried out to ensure the integrity levels have not been affected.
Some hope.
Testing of cylinders as per PED's is rare enough (far too expensive - try keeping a staight face when, on your initial service, explaining to a punter his 100 plus units and priming cylinders are years out of date!) So then try (Potentially) to advise a business shutdown while a room/s is/are integrity tested? Strewth, imagine how popular a service contractor is when that subject is brought up! Foxtrot Oscar is the usual response.
And thats how much "integrity" rules and regs have for a punter when mirrored against a balance sheet. Sad but true. But thats what we as service providers are faced with daily regardles of liability issues.
Ansul R102 Kitchen Suppression Enthusiast