Room integrety testing should be carried out prior to installaton of any gas extinguishing system and at intervals as per BSEN 15004:1 2008. However following any works which may have breached a compartments integrity, testing should be carried out to ensure the integrity levels have not been affected.
Some hope.
Testing of cylinders as per PED's is rare enough (far too expensive - try keeping a staight face when, on your initial service, explaining to a punter his 100 plus units and priming cylinders are years out of date!) So then try (Potentially) to advise a business shutdown while a room/s is/are integrity tested? Strewth, imagine how popular a service contractor is when that subject is brought up! Foxtrot Oscar is the usual response.
And thats how much "integrity" rules and regs have for a punter when mirrored against a balance sheet. Sad but true. But thats what we as service providers are faced with daily regardles of liability issues.