Manual release controls for electronically secured doors
« on: March 22, 2017, 01:04:25 PM »
Afternoon

We have a construction company stating that some of our electronically secure doors that are located on a means of escape do not require manual release controls (green break glass units) as they failsafe on fire alarm activation.

Is this in line with BS 7273 Part 4 requirements?

Many thanks

Offline William 29

  • Hero Member
  • *****
  • Posts: 581
    • http://www.tfsltd.net
Re: Manual release controls for electronically secured doors
« Reply #1 on: March 22, 2017, 01:27:54 PM »
Er..nope

Offline hammer1

  • New Member
  • Full Member
  • *
  • Posts: 157
Re: Manual release controls for electronically secured doors
« Reply #2 on: March 22, 2017, 01:40:46 PM »
Er..nope

Thought not... thanks for prompt reply.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
Re: Manual release controls for electronically secured doors
« Reply #3 on: March 22, 2017, 02:35:37 PM »
Just point them at the building regs - AD B covers this

Offline hammer1

  • New Member
  • Full Member
  • *
  • Posts: 157
Re: Manual release controls for electronically secured doors
« Reply #4 on: March 24, 2017, 02:51:26 PM »
Just point them at the building regs - AD B covers this

They have stated only 2 of the 3 requirements need to be implemented in reference to ADB (section 5.11)?

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Manual release controls for electronically secured doors
« Reply #5 on: March 27, 2017, 03:45:04 PM »
Don't know where they get that from ....

5.11 basically says electronically locked doors should release on

a. fire condition
b. loss of power or
c. activation of a manual release unit.

There's no 2 out of 3 as far as I can see.

Re 7273-4 an emergency manual release is needed directly in line with the power to the locking mechanism in case the for whatever reason, the automated signal from the fire alarm should fail.
CTA Fire - BAFE SP203 - F Gas Accredited - Wireless Fire Alarm System Specialists - Established 1985 - www.ctafire.co.uk
Natural Born Cynic

Offline Mike Buckley

  • Hero Member
  • *****
  • Posts: 1045
Re: Manual release controls for electronically secured doors
« Reply #6 on: March 27, 2017, 05:58:58 PM »
Wilful misreading of the document?
The presence of those seeking the truth is infinitely to be preferred to those who think they've found it.

Offline David Rooney

  • Hero Member
  • *****
  • Posts: 891
    • http://ctafire.co.uk
Re: Manual release controls for electronically secured doors
« Reply #7 on: March 28, 2017, 12:19:14 PM »
Probably ... it would also be interesting to hear their definition of "failsafe" as I suspect it will be different from the definition within 7273-4 ....

it would also be handy to know the 7273-4 category of each door .....