Author Topic: Electronic door locking devices - link to the the fire alarm?  (Read 53917 times)

Offline shaunmckeever

  • Jr. Member
  • **
  • Posts: 86
Can anyone advise me on electronic door locking devices (not magnetic door hold open devices). Should they be linked to the fire alarm system?

I am aware that some fire authorities have local guidance on this issue but I cannot locate any definitive national guidance. What is the problem if the system is not linked to the fire alarm system so long there is a manual over-ride button and the device fails safe on loss of power?

Can the manual over-ride be seen as a key albeit not in the usual sense?

Any advice gratefully received, thanks.
Shaun

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
Electronic door locking devices - link to the the fire alarm?
« Reply #1 on: March 31, 2006, 01:18:14 PM »
An escape door should be able to be opened with one simple action.

Having a button then a lever handle is two.

Personnaly if the lock is a maglock or similar (opens if power cut) and there is an electric panic bar fixed to the door (that cuts the power directly to the lock - not via the control panel) then this is the same as a conventional panic bar so no need for any interconnection.

Offline shaunmckeever

  • Jr. Member
  • **
  • Posts: 86
Electronic door locking devices - link to the the fire alarm?
« Reply #2 on: March 31, 2006, 01:22:57 PM »
Hi Brian

Thanks for your reply. There is no lever handle to operate. It is just a steel plate push door to open.

Offline wee brian

  • Administrator
  • Hero Member
  • *****
  • Posts: 2424
Electronic door locking devices - link to the the fire alarm?
« Reply #3 on: April 03, 2006, 01:34:49 PM »
So its essentially the same as a conventional, mechanical, panic bar.

If thats the case then I don't see a need to connect it to the alarm system.

Offline Simon M

  • Newbie
  • *
  • Posts: 13
Electronic door locking devices - link to the the fire alarm?
« Reply #4 on: April 06, 2006, 04:21:22 PM »
In my business we use them extensively to stop theft from the shop floor.  To ensure they are available for use we have push bars to keep them close when the magnets switch off when the fire alarm sounds, we also have the green BGU just in case.  

I am aware that the FIre Authority in Sheffield won't allow them.

If you need more info let me know.

Simon

Offline Mr. P

  • Hero Member
  • *****
  • Posts: 685
Electronic door locking devices - link to the the fire alarm?
« Reply #5 on: April 07, 2006, 08:36:13 AM »
There  are 2 issues here, Fire & Security.  Where the door is secured by electronic means, this is to fail safe - open.  Usually a swipe card system is used for entry /exit allowing control and monitoring of people.  Overide such as BGU make it a one operation exit unit in emergency.  It does not need to linked into fire alrm system.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Electronic door locking devices - link to the the fire alarm?
« Reply #6 on: April 07, 2006, 09:09:39 AM »
Take a look at the IFE website- publications. Graham Shiel authored  a document which was adopted by the IFE and CACFOA and thereby became the basis for most brigades policy notes.

To see an excellent interpretation of the guidance have a look at the following link:

http://www.ucl.ac.uk/efd/maintenance/construction/fire/PDF/Access-SecuritySystems-Means_of_Escape.pdf

Heres the information from the IFE publications list:

“IFE 13 Guidance on Acceptance of Electronic Locks to Doors Required for Means of
Escape by Graham Shiel BSc(Hons), GIFireE (£9.00)
The pressure on authorities to accept an increasing level of security on doors required for means
of escape will persist for the foreseeable future, as crimes against property and people increase.
The past stance of requiring doors to be freely available in all situations, can now be re-examined
as advances in technology offer alternatives. In which circumstances, and to what extent we are
prepared to accept electronically secured means of escape is a matter for comprehensive debate,
but this guidance will allow new options to be considered.”

Offline val

  • Full Member
  • ***
  • Posts: 234
Electronic door locking devices - link to the the fire alarm?
« Reply #7 on: April 08, 2006, 09:39:51 AM »
Graham Shiel's work was very good at the time but is getting a bit long in the tooth now. The widespread use of these  devices, sometimes for conveinience rather than any real need, cobbled together systems, time delays and very poor management and training (always denied but virtually guaranteed), mean that FRS are constantly being challenged. We have moved a long way from the 'imediately openable' principle. I would like to see how South Yorkshire FRS have been able to maintain their position.
We all wait with baited breath for Colin Todd's, et al, standard on these devices. (Hopefully it will be a management and usability code rather than a simple technical specification.

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Electronic door locking devices - link to the the fire alarm?
« Reply #8 on: April 08, 2006, 10:46:33 AM »
Val
I fear that it will not. Hopefully CT himself will respond to your point himself but in case he doesn't  heres a selection from an email I received after commenting:

"BS7273-4...... will only deal with the electrical interface with door hardware, but no the hardware itself, etc. The purpose of the code is, as it were, to make sure the signal is delivered reliably.......".

Or maybe there are other draft standards in progress?

Offline val

  • Full Member
  • ***
  • Posts: 234
Electronic door locking devices - link to the the fire alarm?
« Reply #9 on: April 08, 2006, 12:38:52 PM »
Kurnal

Thankyou for the clarification. If that is the case then there is a gap for CFOA (after all they want to be the voice of the FRS), to redraft Graham's work and set a national benchmark. The ODPM's guides do contain some fairly good advice on this subject but it will need expanding with more detailed arguments to cover all aspects of this market/trend. Unfortunately, the ODPM guides always have to have the qualification of 'should' or 'in most cases' which leaves that chink of light for argument and we are all back at the beginning again.

Offline shaunmckeever

  • Jr. Member
  • **
  • Posts: 86
Electronic door locking devices - link to the the fire alarm?
« Reply #10 on: April 08, 2006, 02:08:48 PM »
I love this forum it is so good for debate and a great source for learning.

I have a copy of LFB's guidance note. I have also contacted several brigades directly regarding this issue. It concerns me that there is no consistency of approach between brigades.  I can foresee a fire risk assessment carried out on a building which accepts the use of electronic door locking devices not linked to the alarm where an IO from one brigade will look at the assessment and disagree with the use of the device and a similar assessment in another brigade where the use of the device will be acceptable to the IO.

This is just one issue. Whether an IO can make a judgement as to the suitability and sufficiency of a fire risk assessment where there are going to be inconsistencies in approach by different brigades over several other issues needs to be addressed.

Offline AnthonyB

  • Firenet Extinguisher Expert
  • Global Moderator
  • Hero Member
  • *****
  • Posts: 2479
    • http://www.firewizard.co.uk
Electronic door locking devices - link to the the fire alarm?
« Reply #11 on: April 08, 2006, 10:10:38 PM »
Some flexibility with mag lock exits is sometimes sensible, but there are times when you would need to insist on all three failsafes - break glass, power loss & fire alarm relay - the situation that I normally require these is any exit which, by virtue of the nature and number of persons who may have to resort to it, needs to be panic proof. If the premises insists on a mag lock & panic bolt combination, it isn't panic proof if you have to remember to smash a glass before your weight on the panic bar opens the door - we don't want to regress to the fatal key in glass fronted box type situations of Summerland & Woolworths.
Anthony Buck
Owner & Fire Safety Consultant at Fire Wizard


Extinguisher/Fire History Enthusiast

Fire Extinguisher Facebook Group:
http://www.facebook.com/group.php?gid=65...415&ref=ts
http://www.youtube.com/user/contactacb
https://uk.linkedin.com/in/anthony-buck-36

messy

  • Guest
Electronic door locking devices - link to the the fire alarm?
« Reply #12 on: April 25, 2006, 09:48:04 PM »
What is accepted practice when it comes to 'security' applications such as prisons, mental health units, and care homes?

Is it possible/acceptable for a magnetically locked door (final exit or otherwise) without a BGU override?

If so, is there any written guidance anywhere (cos I can't find it)

Offline kurnal

  • Hero Member
  • *****
  • Posts: 6489
    • http://www.peakland-fire-safety.co.uk
Electronic door locking devices - link to the the fire alarm?
« Reply #13 on: April 25, 2006, 10:30:49 PM »
Dont know if this may be of any use messy- Like you I was struggling to find anything definitive. This was a secure school for teenage children. Sorry for the length of the posting- if its not of use I guess Chris can delete it!

Xxxxxxx xxxxxx School- Specific risk assessment for the use of security devices on exit doors

A- The problem- hazards

The current arrangements for the security and availability of exit doors are unsatisfactory and require urgent review.

1- The system may be insufficiently robust as the doors are secure and can only be opened on the operation of the fire alarm system. Fire is by no means the only reason for possible evacuation of the building. Where electronic locks are fitted all the building codes consider it necessary to provide some mechanism for the door to be used independently of the operation of the fire alarm. Persons needing to leave the building in an emergency may be unable to do so unless their local fire alarm sounder is operating.

2- The doors appear to be linked to the local sounder circuits of the fire alarm system so the doors re-lock on silencing the alarm- making testing very difficult and leading to difficulty during fire evacuation procedures.

3- Testing is not carried out in accordance with and at the appropriate frequencies in accordance with the relevant standards

4- The school is completely unstaffed during holiday periods and false alarms during this time leave the building insecure. The current configuration of all alarms across the site leaves all buildings potentially insecure if an alarm operates in any one.

5- Due to the policy of total evacuation, it becomes inflexible for the senior manager to reallocate any members of staff to the areas of greatest need as all will be evacuating the students under their care to the assembly areas and none will have information on the location or nature of the emergency. Roll calls will be taken for all buildings and this may divert attention from the areas of greatest need

6- All students and staff will face the disruption caused by an alarm in a separate building and may suffer unnecessary distress


The Fire Authority, in their letter dated 28 February 2005,   recommended a system incorporating emergency green break glass door release mechanisms in accordance with  “section 3”  of the “guidance on the acceptance of electronic locks required for means of escape” published by the Institute of Fire Engineers and CACFOA.
This advice would create potential difficulties for the school. There is an ongoing problem of the malicious breaking of alarm call points- recently an average 6 per month. The students are closely supervised but additional break glass devices would become an obvious target for malicious operation. This would very quickly create problems for the staff as security and supervision of the pupils is paramount due to their special needs. Such a system would not offer any impediment to a child wishing to abscond and may jeopardise the ability of the school to provide the appropriate level of care and
supervision. Malicious operation of the door break glass point would allow escape without operation of the alarm – thus further jeopardising the care of the child.

B- Persons at risk
The staff, students and the security of the business are placed at risk as a result of the current arrangements

The situation at Xxxxxxx House and other similar establishments is not unique- similar means of escape and security conflicts are encountered in some care homes, some types of hospital and some types of childrens remand homes. In such cases solutions are normally found by risk assessment and liaison with all parties involved.

C- Available guidance and existing control measures
There is considerable guidance on acceptable measures in a range of building design codes. Whilst none of them offer specific solutions, they all indicate a need for a flexible approach taking into account the circumstances of the case. Such documents include:
•   The HTM series (Hospital technical Memoranda) ,
•   The draft guide to fire precautions in existing residential care premises,
•   Building Regulations approved document B,
•   BS5588 series.
•   Children’s Act 1989 ,
•   National Standards under the Care Standards Act 2000
•   Guidance on the acceptance of electronic locks required for means of escape
•   Home Office 1990 Fire Standards in Prison establishments
However whilst all of the above documents consider the conflict between availability of exit and door security, in most  cases the security considerations are in respect of persons breaking in from the outside. Only the “guidance on the acceptance of electronic locks” properly considers situations where for internal security reasons, persons inside the buildings may not be given immediate access to a mechanism which over rides the electronic door lock. (in section 4). It would not be reasonably practicable to implement the solutions suggested in this part of the document in this case due to the character and nature of the building.
Whilst none of these documents offer specific solutions appropriate in this case, they all suggest the need for risk assessment, liaison and agreement in special cases, between all parties with responsibility to oversee the fire safety measures at a premise.

All of the technical documents listed above do share some common ground. For example all documents:

•   Do not consider an electronic door release on its own to be satisfactory as the sole means of opening a fire exit door without some other measure which may include a range of measures from  an opening mechanism to video surveillance and remote control
•   do not consider a mechanism requiring the use of a key to be acceptable,
•   most do not support the use of number key pads on the risk side of a door.
•   They do not recommend the connection of door release mechanisms to local sounder circuits and if this is the only way, then latching relays should be used.
•   All components of the system to fail safe (Door open) and be designed, constructed and installed to a life safety standard and not breaching the recommendations of other standards eg BS5839.
•   Electronic security devices must fail safe in the event of system or power failure- i.e. any failure causes the door to unlock.


Site specific factors- control measures

The special circumstances at the school to be taken into account are as follows:
•   Xxxxx building apart, the buildings cannot conform to current design codes- the sleeping accommodation on the first floor of A block is served by two staircases, one being external, the main one having a number of rooms opening directly into it, without fire doors to a good standard. The fire resistance of elements of structure in the portacabin units cannot be accurately  assessed
•   In xxxxx  Block there is two way travel though not in a protected route- and an unprotected  dead end condition on the first floor teaching corridor though this is covered by automatic detection
•   New fire alarm and detection systems have been installed in xxxxx Block - radio linked to an L1 standard. This system is fully addressable and has been configured to link in all other alarm panels across the site- though not addressable. A mimic panel has also been provided in a separate location.
•   The students all have special educational needs and a secure environment is essential. Most are fully dependent on the staff for leadership and instruction in case of fire, though none of the current students have significant sensory or mobility impairment.
•   Staffing ratios are very good with an average of 5 students per staff member under constant supervision at all times day and night
•   Staff members have all received training in fire procedures
•   It is most unlikely that in the event of a fire the students would need to use a fire exit door outside the direct supervision of their member of staff
•   Visitors and contractors are not allowed unaccompanied access to the building.
Recommended additional measures to be taken
A.   Each exit door should be provided with a means of opening by staff independent of the operation of the fire alarm. In this case the doors may be secured by mechanical keypad on the side from which escape is needed. Alternatively, subject to compliance with the relevant life safety technical standards, a swipe card or tally system would also resolve the security / escape conflict in this case.

B.   The system should be reconfigured such that the door lock mechanisms are correctly wired back to the main panel rather than local sounder circuits, or if this is not possible, use latching relays of the life safety standard (see guidance document). It should be possible to test the door release mechanisms without the need to maintain the operation of the sounders.

C.   The system should be reconfigured to allow the alarm systems in the out buildings to be tested without the alarms sounding across the whole site.

D.   Whatever solution is adopted, it would be wise to incorporate the facility of access via use of a key from the outside of an exit door, so in the event of persons being trapped within the building, staff or firefighters can access the door from outside. This is relevant at the School as due to the age, character and nature of the building passive fire precautions can never conform to modern standards.

E.   Regular staff training should be carried out to cover the reasons for the design and use of the access control system and should any combination be changed robust means of ensuring staff awareness of the new details

F.   The evacuation procedures should be reviewed – consider the current full site wide evacuation strategy, the effective use of the alternative control position at the mimic panel, and communications with staff in an emergency

G.   The alarm systems should be tested in accordance with BS5839. Daily checks, weekly tests and periodic inspection and test by an engineer should be carried out. For the older panels, during the weekly test it is important to check each alarm panel by operating a call point in each zone. The new installation should be tested in accordance with the manufacturer’s specification- more recent panels have much improved fault monitoring and reporting systems.

H.   The alarm system should be monitored by a call centre.

All of the above points should be discussed and agreed with the enforcement agencies and alarm engineers before commencing work. It is presented as a reasonable compromise between the conflicts of escape and security in this special care environment

Offline jokar

  • Hero Member
  • *****
  • Posts: 1472
Electronic door locking devices - link to the the fire alarm?
« Reply #14 on: April 26, 2006, 09:24:25 AM »
Messy, I did some work for The Government, FRA's in Crowm and County Courts.  The approach that the Government wanted was no electronic locks but to have BGCP that actuated the door.