Carrying out a design review for a new warehouse where ESFR sprinklers will be installed, I assessed the design against TB209- 2004.
I noted that the areas beneath a large mezzanine with a floor height of 6 metres had spray pattern XHH sprinklers specified and that no boundary conditions are specified between the two systems.
TB209 recommends ESFR under a mezzanine where the floor height exceeds 4.5 metres, and that where different systems are installed side by side that boundary conditions are applied.
When I queried it with the designers and the insurers they were not in the least concerned and said that this part of TB209 is impracticable, and "nobody does it."
I can see the difficulty of installing ESFR inder the mezz with all the additional obstacles and steelwork to have to work around- but there must be a reason for this requirement being included?
Any advice gratefully received