Wiz this is your opinion and but, I do feel that it's not correct to use spurs on a loop. As I said earlier how would you feel tracing a cable fault etc.. finding a bucket load of spurs on a system (and it happens). Not to sound smart but you are correct in saying that it's not mentioned on BS5839 (we don't use these regs anymore in a lot of cases our regs are slightly higher), but if is not mentioned in BS or any other standard does that mean that its ok, my opion is that it is not ok to use spurs in any case on a loop at the end of the day you are dealing with life and to me this is the way it is and that it isw not ok to use spurs under any case. And one of my reasons for this is how may time have you seen a spur with no isolator, it happens so often its not funny. "I maintain you shouldn't tell anyone that something is categorically wrong, when it isn't." I would tend to agree with this comment but I find that spurs are not correct and would not let any of my staff use them, to be honest I would sack them.
Irishfire, how nice to have a considered discussion with you. Yes, I agree that you are perfectly entitled to demand that your staff do not use spurs on addressable systems. However, I maintain that it does not mean that anybody else using them is wrong or incompetent or a 'cowboy' in doing so.
Despite what you might think of the technical Standards, these are probably the only thing (apart from manufacturer's specific instructions in respect of their own equipment) that we can all use to determine and hopefully agree exactly what is and what isn't 'allowed'.
I agree that the use of 'spurs' can sometimes make fault-finding a bit more difficult. However, using them in a system, with due regard to BS recommendations, does not necessarily make such a system less reliable or less good or less compliant than every system wired as a loop. I welcome any discussion on this opinion.
The reason I have 'highlighted' this matter is because I believed the comments made about the use of 'spurs' were wrong and misleading. Many people use this site to 'learn' new things and it is important that we all try to ensure that anything that is stated as a 'fact' rather than an opinion is 100% correct.
People often tell me that something has to be done a certain way because it says so in the Standards. When I ask them to direct me to that particular recommendation in the Standard, they then advise me that, in fact, they haven't seen it themselves but were actually 'told by someone else' that 'they had to do it this way' and then assumed that this was the only way detailed in the Standards. I think this is similar to 'Chinese whispers'.
I hoping that you will now agree with the conclusions that I have now reached about this matter as follows:
1) It is o.k., both technically and also in respect of the recommendations in BS5839 part 1 2002, to have radial spurs connected to addressable loops as long that any single wiring fault does not affect the protection covering an area of a maximum of 2,000m2.
2) That in your opinion you do not like the use of radial spurs to addressable loops sytems. However you can't say it is 'incorrect' to use them
3) Anyone using radial 'spurs' on an addressable loop is not necessarily incompetent or a 'cowboy'