To answer in order:
I informed them that the system werent compliant and the response was "find some legislation" and "once we do the weekly check, that will cover us".
There are no out of hours - we are 24/7
Kurmal - you have described with uncanny accuracy the situation surrounding one of our previous H&S managers. One thing I do have is time to document, I take copies home and the plan is to make them sign for them or I will pass them to the department manager and he can sign them.
The fire brigade do call around periodically as we are a high risk site but they only are familiarising themselves so they dont fall in the pit again. They rarely pass comment on the building or fire alarms. They do occasionally ask to see the fire alarm but we only show him the control panel for the server room HFC system - he sees a 24V panel and is happy.
"Penny wise, pound foolish" describes this guy to a tee
Another slight lie from mgmt was that there is nothing flammable in one half of the factory, the oil is all water based. Then I discover that we have 20,000 gallons of warm mineral oil sloshing about the place!
The prospect of 40K on a fire alarm and 25K on emergency lighting didnt go down too well

Thanks for your comments.